David Lord wrote:
I had maxpoll set at 10 when I first setup my network but sometimes
at that poll rate combined with daily temperature variations offsets
would gradually increase both in +ve and -ve directions. This could
clearly be seen in mrtg graphs. Solution was to reduce maxpoll to 7
or 8. I never thought of this as a bug. There was a daily variation
depending on season and a variation due to system load.

This has been with NetBSD 1997 to date and a period of a few years
when running FreeBSD. Currently NetBSD-6, ntp-dev-4.2.7p401, four
of the servers are in the pool.

I think we need to distinguish if there's a computational problem in the code due to a rounding error, range overflow, or similar, or a systematic problem, where ntpd is in general unable to apply adjustments fast enough to compensate frequency drifts varying fast with temperature changes.

Which the former can be fixed in the code once the wrong code has been detected, the latter can only be changed by redesigning ntpd's behavior.

As far as I know long polling intervals are used preferably to increase the accuracy of the drift measurement. For example, if you want to see if your wrist watch goes fast or slow, you can't see this properly if you check it once per minute. However, if you check it after one day you see how many seconds the wrist watch has gained or lost.

However, as I understand this, this only yields proper results if the frequency doesn't vary too much over the measurement interval.

So if ntpd only compares the time once every 1024 s the frequency may have increased and decreased again during this interval, e.g. due to varying CPU load, without this being noticed by ntpd. So the correction computed in such case is probably not optimal.

From my understanding it would be better if ntpd polled in shorter intervals to detect if the frequency drift is constant, or not. If it is not it could decrease the polling interval to react faster on frequency changes.

However, changing the latter would need some reengineering of the control loop.

Martin
--
Martin Burnicki

Meinberg Funkuhren
Bad Pyrmont
Germany