On 21/05/14 19:08, E-Mail Sent to this address will be added to the BlackLists wrote:
William Unruh wrote:> BlackLists wrote:


Otherwise make sure that the cable is terminated with the appropriate
resistance. (50 ohm I believe for Cat 5). Note that source had better be
able to drive that impedance or the signal will be very small.

I believe it is more like 100 ohms at Ethernet frequencies, but at RS232 frequencies, it will be very frequency dependent and impossible to match across the full bandwidth.


RS232 was only designed to drive 50ft.
The capacitance of "RS232 spec cables" prohibits them from working at 1000ft.
The Cable and Load have to be less than 2500pf
RS232 Receivers include termination in the 3k to 7k ohms range.
RS232 Driver impedance must be 300 ohms or greater.

RS232 is designed to operate cables under conditions where the reflections make them look capacitive, so both the source and load impedance are well above the line impedance. That means there is no ringing, so no false edges.

RS232 Drivers are limited to 500ma max drive.

I'm fairly sure that is impossible with the specified source impedance and open circuit voltage.

RS423, using similar levels to RS232 allows much longer lines for slower signalling rates, although it does require explicit slew rate limiting at the driver.

RS232 is very conservative. Also a lot of the limitation are probably based on its being unbalanced.