HI Jim,

The CC is sure suspect. 
You didn’t mention what the battery voltage is. 
Those CC have a hard PV watt input limit.

You can try and set it back to factory default and then reprogram, sometimes 
that works.  

I don’t use the FM-60, but always the FM-80 because of the fan replacement.  
the 80 takes 3 minutes, the 60 takes 2 hours. 

jay

> On Apr 23, 2024, at 6:00 AM, Jim Gowdy via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> I'm troubleshooting the solar aspect of a small offgrid 120v outback system 
> and need some opinions.  The customer was complaining that the generator was 
> running too much so I went out to their property and investigated.  The solar 
> array consists of 16 total panels (4 strings of 4).  At the combiner box, I 
> took the voltage and amperage reading of each string and found the 
> following......BREAKER 1 (85VDC/8.87A) BREAKER 2 (84.5VDC/8.9A) BREAKER 3 
> (.03VDC/0A) BREAKER 4(85VDC/8.89A).  Breaker 3 string was not producing and 
> so I did a fix and then read (87.1VDC/8.43A).  After reviewing the online 
> monitor since that fix from a few days prior I'm realizing that the first day 
> after had 4.5KWH production, second day had 0.7KWH production, and yesterday 
> had 0.3KWH production.....sun has been out without clouds.  The 60A Outback 
> charge controller shows there is PV voltage, but noticed it was in "silent 
> mode" a good amount of time.  Charge controller is old, but all the other 
> equipment was updated about a year and a half ago.  I was wondering if there 
> is a way to diagnose if the charge controller is bad without just replacing 
> it and what does it mean when it's in "silent mode".  Another side note is 
> that their generator threw an AGS fault code on the MATE3 controller and 
> found that the generator has problems so I ended up turning from "auto" to 
> "off"
> -- 
> Jim with Gowdy Electric
> Cambria, Ca 93428
> business  805 927 2630
> cell  805 975 5279
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to