Nick:

Here's my best guess: The X240 is configured to work with power legs with 180 degree phase differential. A 3 phase source has 120 degree phase differential. This 120 degree phase differential shows as some degree of direct short to the source.

Solution: I would forego the X240 and change the stacking configuration to Classic stacking. Eliminate any shared neutrals to avoid neutral over-current.

William Miller


At 08:09 AM 7/29/2008, you wrote:
Hello good folks in the RE world! An off grid customer of mine has a VFX Quad Stack wired exactrly like page 20 in the FX manual, including the X-240 balancing transformerconnected to the panel output legs. He has been feeding it with two legs of a three-phase diesel generator. IS THIS A COMPLETE NO-NO??? HE KNOWS THAT IT WILL RESULT IN AN UNBALANCED GEN OUTPUT, BUT SO FAR IT HAS BEEN WORKING OK, BUT WITH THE FOLLOWING GLITCH: WITH THE GENSET OFF------THE OUTBACK POWER PANELOUTPUT BUSSES ARE BOTH ENERGISED ONLY WHEN THE x-240 BREAKERS ARE ON. AS SOON AS THE GENERATOR STARTS (AGS SYSTEM) THIS 20 AMP DOUBLE BREAKERSEE PAGE 20, X-240) TRIPS IMMEDIATLEY, LEAVING HALF THE LOADS WITHOUT POWER (NO OUTPUT FROM THE LEG 2 INVERTERS TO THE HOT 2 OUT BUSS) i'M BAFFELED, COULD SOMEBODY PLEASE EXPLAIN THIS SITUATION TO ME SO THAT i CAN HELP THEM OUT? Another electrician told them that a buck/boost transformer (on the gen output?)would be the fix. Thanks a bunch in advance for your help in this serious matter. Nick Houser Off Grid Services, Powell River, BC


_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Reply via email to