Bill,

That is a great point. As it stands, the box ahead of the residence does contain a main breaker. If we get rid of that breaker and turn it into a lugs only panel, it would satisfy the requirements. I wonder how that would pan out, since the wiring runs through this other building.

Thanks,

Drake


At 12:49 PM 7/31/2008, you wrote:
Content-Type: multipart/alternative;
        boundary="----=_NextPart_000_006F_01C8F303.83492700"
Content-Language: en-us

Drake,

690.64 relates everything to the service disconnects. All the rest of this is semantics. As long as the PV connection is upstream of the service disconnect (i.e. in between the service disconnect and the service meter), it is considered a line side service connection.

If there is no way to turn off the residential service in the panel with the “feed-thru” lugs, there is no service disconnect for the residential service yet. That way if the connection were on the line side of the first service disconnect for the residence (one of two services at the site, both coming from the same service drop­to get all the semantics proper), it is considered a line-side connection. So what is it….?

Bill.

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Drake Chamberlin
Sent: Thursday, July 31, 2008 9:13 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Gray code area

At 03:24 PM 7/30/2008, you wrote:

According to the two paragraphs above, the commercial building has two commercial services??? One will receive PV and one will not??

One service is for the commercial building and one is for the residence. There is one service drop to two meters. Both services will be fed PV.


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
303-328-5533
_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
303-328-5533 
_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Reply via email to