I have installed many Fronius grid-tie systems having a single inverter, but recently installed a dual 3K inverter system and are having all kinds of problems with the inverters not connecting to grid due to out-of-range grid voltage or cycle errors. If we shut down either inverter, the remaining inverter usually works fine. The only thing we can identify is the electrician may have under-sized the new feeder wiring as we had to run over 150 feet to the first breaker panel in a barn, which was another 150 or more feet to the main panel and meter base. The sub-panel also serves a large well pump that supplies several different buildings and this may be causing some voltage sags.
We are looking into up-sizing the feeders, but I am still wondering if there are other issues or concerns when you have multiple inverters side-by-side at the end of a long grid connection. Thanks, Jeff Yago _____________________________________________________________ Netscape. Just the Net You Need. _______________________________________________ List sponsored by Home Power magazine [email protected] http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org