If you use multiple FW-1000s and the FN-DC to tie all three shunts together, you can wire the entire inverter side with 3' cable sets. Greatly simplifies your wiring, and ensures each inverter sees similar voltage drop.
Probably want to consider running the FWs horizontal, to act as one big "gutter" otherwise the top inverters need ladders to access ;-). I suggest three FW-1000s instead of 2+1 FW-500, as you probably will want to add some charge controllers, which are easiest to mount on the open FW-MP backplate (OB's charge controller brackets don't work when the FWs are sideways. Argh). The AC end is simple -- just input and output breakers. If you want to add bypass capability (a good idea) that has to be done external to the OB equipment when you go beyond 8 inverters. If you want a itemized parts list, contact me off-list and I'll work something up. Phil Undercuffler Director, Battery-based and Off-grid Distribution Sales Group Conergy Our World Is Full of Energy 1730 Camino Carlos Rey Suite 103 Santa Fe, NM 87507 [EMAIL PROTECTED] Direct | 505.216.3841 Toll Free | 888.396.6611 x4841 Fax | 505.473.3830 www.conergy.us -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of jay peltz Sent: Tuesday, October 21, 2008 7:21 PM To: RE-wrenches Subject: [RE-wrenches] 10 stack outback HI All, Does anyone have a parts list and wire lengths for a 10 stack outback system? this is the vertical 10 in a row, not 21/2 quad stacks. I can do it but thought someone else must have all this done before, many thanks, jay peltz power _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org