I think that the calculation goes as follows:

 

(1) For residential PV systems, the bus can fed at 120% of its rated value:
1.2*225A=270A

(2) The main breaker limits the feed from the utility to 200A

(3) This leaves 70A for the PV system

 

- Peter

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _____  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Christopher
Freitas
Sent: Thursday, December 04, 2008 2:51 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D 225A load center

 

Ahhh - I think I get it - you get the 20% of the 200 amps (so 40 amps) + the
extra 25 amps because the buss is only running at 200 amps?

 

I just saw you emailed me.  

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

 <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

 <http://www.outbackpower.com/> www.outbackpower.com

  _____  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Brearley
Sent: Thursday, December 04, 2008 11:41 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D 225A load center

 

It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, "Christopher Freitas" <[EMAIL PROTECTED]>
wrote:

How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 225
amps is 45 amps - and even with "rounding up" it only gets you to 50 amps.  
 

Christopher

 
Christopher Freitas
Director of Research and Development 
OutBack Power Systems, Inc.
[EMAIL PROTECTED]  <mailto:[EMAIL PROTECTED]>
<mailto:[EMAIL PROTECTED]> 
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE 
Arlington WA 98223 USA
www.outbackpower.com  <http://www.outbackpower.com/>
<http://www.outbackpower.com/> 

  _____  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]
<mailto:[EMAIL PROTECTED]>  On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 8:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center




Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar

 

MESSAGE CONFIDENTIALITY NOTICE:

This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential,
and may also be protected by attorney-client or other privilege. If you
believe that it has been sent to you in error, please do not read it. If you
are not the intended recipient,you are hereby notified that any retention,
dissemination, distribution, or copying of this communication is strictly
prohibited.  Please reply to the sender that you have received the message
in error, then delete it. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to