Jerry -

A line tap typically occurs between the utility meter and the main breaker - 
not after the main breaker on the load side. It seems that you are describing a 
load side tap which follows the 120% rule under 2008 NEC; I might be 
misunderstanding the situation. Please clarify. There are few folks out there 
who are able handle these large commercial grade interconnections and I think 
it is well worth discussing.

Good luck! -August 



 August Goers


Luminalt Energy Corporation
4000 Irving Street 
San Francisco, CA 94122


Office:  415.564.7652
Mobile:  415.559.1525
[EMAIL PROTECTED]
www.luminalt.com





________________________________
From: William Miller <[EMAIL PROTECTED]>
To: RE-wrenches <[email protected]>
Sent: Friday, December 5, 2008 4:11:15 PM
Subject: Re: [RE-wrenches] load side taps and NEC 240.21

Jerry:

At a recent John Wiles seminar, John declared that this scenario is not a 
tap and is therefore not covered under the tap rule.  This was news to me, 
but Wiles is considered some sort of guru in compliance discussions.

William Miller


At 03:43 PM 12/5/2008, you wrote:

>Wreches,
>
>
>I have a system where we are tapping onto the bus bars of a 1200 amp panel 
>fed by a 1200 amp main breaker.  The easy place to tap onto the bus bars 
>is the load side of the breaker using the existing bolts.
>
>
>The inverter and utility fused disco are about 200 ft away, and the tap 
>conductors travel about15ft in EMT conduit before leaving the 
>building.  After that the circuit is outdoors.  NEC 240.21(B)5 allows taps 
>of unlimited length for conductors located outside of a building, except 
>at the point of load (in this case supply) termination.
>
>
>Can 20ft of conductor inside the building be covered by being "at the 
>point of load termination", or do I have to comply with NEC 240.21(B)2 and 
>have an OCPD within 25'?
>
>
>The construction foreman for this project is buddies with the inspector, 
>so getting a signed permit won't be a problem but I want this to be a code 
>compliant system.  Can anyone lend some insight to the spirit of 
>240.21(B)2 and 5?
>
>
>Sorry if this has been discussed before, but searching didn't yield any 
>results.
>
>
>Best,
>
>Jerry Caldwell
>
>Recurrent Energy
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: [email protected]
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to