Hi William - Might try running the inverter in question on its own, (set it back to split-phase master) and see if it charges OK then. Also worth first monitoring that inverter on the SCP (set the SCP to the home screen of the affected inverter) and see what its "status" is when trying to charge.
Once you have that data a call to the tech support line can get some more pointers. Cheers, Mark Mark Edmunds Xantrex Technology Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of William Miller Sent: Saturday, December 20, 2008 10:15 AM To: RE-wrenches Subject: [RE-wrenches] Dual XW glitches Friends: We have installed a number of single XW installations but only one dual XW. The dual system is giving us some problems. When the generator is started, both inverters will charge, but aft a minute or so, the slave will stop charging. This is even with very low batteries where both inverters charging capabilities are needed. Once I observed Inverter 2 trying three times to charge but eventually giving up. Has anyone experienced this? Thanks for your input. William _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org