Kurt,

You definitely need the dedicated branch circuit protection. Beyond that, it's up to your local AHJ. Same for the labeling. Of course, NEC 690.54 and 690.56B do require a label at the point of interconnection.

See Ya!

Marv
Enphase Energy
707 763-4784 x7016

Kurt Albershardt wrote:
--On Monday, December 29, 2008 8:29 AM -0800 Marv Dargatz <[email protected]> wrote:

The NEC provides for, and the AHJs have accepted the use of the connectors as a form of disconnect. Of course, each branch is also connected to a dedicated branch overcurrent device (circuit breaker).

On the DC side, since only one module is connected to each inverter, the connectors also serve as a means of disconnect. The DC wiring does not enter the building, so a separate DC disconnect is not required.

Right, no problems foreseen there.


What specific questions do you have about labeling?

Five small arrays, each on a different structure, feeding one production meter (located on one of the structures or perhaps on a separate outbuilding.) Do I put a small breaker/disconnect (I'm thinking a 2-space 3R panel) on each structure and label (how)?

thanks...





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to