Hello all,
Report from my last visit and some generator forensics. The 240v generator plug was wired for only one leg and terminated at another plugbox on the wall of the shed. This other plugbox had basically fried internally and when disassembled pretty much came apart, carbonized wires. So when I measured the output from the genset under load, at the generator it appeared ok. When the voltage was measured at the FX terminals, with no load, it was ok but as soon as a load was applied the voltage began cycling up and down, presumably as the resistance in the generator wall plug increased. The attempt of the FX to connect AC-In was immediately dropped as the load of the charger kicked in, thus the click after 20 secs. as it attempted to connect then dropped the connection.

I re-wired the genset plug for both legs then wired it into an Outback FW-X240 to balance the output into the FX and everything is now working A-OK. Although the system had previously been working for several months the eventual deterioration of the wiring in the plugbox on the wall led to it's downfall because the FX was only getting half the output from a 3800w generator at best. The generator was improperly wired, by the homeowner presumably, and could have led to a fire. I just wish I had spotted this problem on the first visit but working in a dark outdoor shed with a headlight in -25 C temps has it's limitations.

Thanks to everyone for your input and may the New Year bring us all the sun, wind and water we need to green the planet.

Ron Young
earthRight - Solareagle


On 31-Dec-08, at 10:43 AM, Darryl Thayer wrote:

HI all and Ron
In my previous post I said the inverter FET board, I am wrong, it would have to be the AC board or the generator is running out of frequency spec.

Place a load on the generator, so it runs in power note idle, use your meter to measure the generator frequency, set the inverter to not charge, have no load on the output of the inverter, Try as you have done. The inverter should connect offering very little load. If the same effect, measure the surge current to the inverter using your meter. I think the surge should be very minimul.

Darryl


--- On Tue, 12/30/08, R Young <[email protected]> wrote:

From: R Young <[email protected]>
Subject: Re: [RE-wrenches] Outback VFX input voltage cycling
To: "Christopher Freitas" <[email protected]>, "RE- wrenches" <[email protected]>
Date: Tuesday, December 30, 2008, 1:29 AM
Hi Chris,
My answers appear below:

On 29-Dec-08, at 10:41 AM, Christopher Freitas wrote:
When you tested just the inverter without the
generator running – you stated that there was a noticeable
flicker every 20 seconds –

THE GENERATOR WAS RUNNING, IT'S JUST THAT I TURNED OFF
ALL THE LOADS TO SEE IF THE PROBLEM WOULD PERSIST AND I
FOUND THAT THE RAPID CYCLING OF THE VOLTAGE AT INPUTS QUIT
AND THE VOLTAGE STABILIZED AT ~121V BUT ABOUT EVERY 20
SECONDS, JUST WHEN YOU WOULD EXPECT THE AC-IN TO GET PICKED
UP BY THE INVERTER THERE WOULD BE AN AUDIBLE CLICK, THE
VOLTAGE WOULD SUDDENLY DROP TO ABOUT 110V, THEN IMMEDIATELY
RECOVER TO ~121V. AT NO TIME DID THE AC-IN GET PICKED UP.

When the generator was connected to the inverter –
was the varying AC input voltage viewed on a digital test
meter or on the MATE’s display?

I WAS MEASURING THE AC INPUT VOLTAGE WITH A FLUKE METER AT
THE INPUT CONNECTORS ON THE FX.

Is this a 120/240VAC “split phase” generator
operating with only one inverter on it?  It is possible that
an internal connection in the generators windings has fried
due to overloading one output leg of the generator – its
similar to a bad solder joint where the voltage is OK until
current is pulled and then it opens up.  You might try
putting the inverter on the other leg to see if you see the
same issue.

THIS IS A POSSIBILITY THAT I WILL LOOK INTO. IT IS RUNNING
ON ONE LEG OF A 240V GENSET, NOT THE IDEAL SITUATION.
I'LL BE PUTTING A PSX240 ON IT TO BALANCE THE OUTPUT BUT
WILL FIRST CHECK TO SEE IF IT WILL RUN OK ON THE OTHER LEG
BY ITSELF.


Be sure to check the frequency of the generator when
seeing issues like this – its often the problem.


THAT'S ON THE SHORT LIST, THANKS

Thanks all who have offered suggestions, I'll check
back in with whatever I find out.

Ron Young
earthright - Solareagle




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to