Hi Jay,
You are right. A lot of photos and almost all live shots are from news
helicopters usually showing commercial flat roof fires. Most of the smaller
fires and residential fires are knocked down too fast for reporters to get
to the scene or the news services think are not eye-catching. Most home
fires with steep pitched roof are fought from the ground. The general plan
of attack is to evacuate the smoke, enter the building to save people, stop
the fire at its source, and stop the fire from spreading. Fire people
describe the strategy differently, but it boils down to first save the
people, then save the property, then save the neighborhood.
From a PV contractor's standpoint, we have to design for building inspectors
and firefighters but their needs (or the AHJ's interpretation) are not
always in sync. The AHJ trumps the firefighter. I think that the PV
industry's best strategy is what is being done now. Get the firefighters'
buy-in and let them tell the AHJ what they need rather than letting the AHJ
define what he thinks the firefighters want.
Believe it or not, the situation is getting better at least in California
thanks to Sue Kately, CalSEIA executive director, and others. A year ago,
almost all small residential PV systems could not meet the AHJ's
interpretation of fire safety needs. Now about 7 out of 10 jobs get
permitted.
Joel Davidson
----- Original Message -----
From: "jay peltz" <[email protected]>
To: "RE-wrenches" <[email protected]>
Sent: Thursday, January 08, 2009 7:56 AM
Subject: Re: [RE-wrenches] fire safety vs. fire hysteria
As I follow this thread and just got off a 12 and 12 roof, I wondered how
the fire departments deal with roofs you cannot get to easily?
I've seen lots of photos of firefighers on roofs, but pretty much all
flat roofs or low angle ones.
For example
a metal roof in the wet,
steep roofs
steep roofs in the snow?
ETC.
Just wondering,
jay
peltz power
On Jan 7, 2009, at 1:05 PM, Antony Tersol wrote:
The fire hysteria is relatively easy to deal with - the facts take
care of untruths. As William Miller noted, of greater threat here in
California are the rules being presented by various fire departments
and by the California State Fire Marshall's office.
Among the problems that we have seen (references to the
solarphotovoltaicguideline document):
1. The guidelines are being used in place of regulations. Page 6 is
not read - including:
"This guideline is just that, it is a suggested means of writing a
local ordinance and does not have the force of law."
"...the city, county, or city and county must make express findings
for each amendment, addition or deletion of the state building codes."
"Provisions contained in this guideline do not apply unless
specifically adopted by local ordinance by a local enforcing
agency..."
2. Page 10, section 2.2.1 is applied to all buildings, including
single family residential.
"2.2.1 Access
There should be a minimum six foot (6') wide clear perimeter around
the edges of the roof.
Exception: If either axis of the building is 250 feet or less, there
should be a minimum four feet (4') wide clear perimeter around the
edges of the roof."
3. As William noted, the restriction of 3' from the ridge for
residential (page 10, 2.1.2) will eliminate or severely constrain a
very high percentage of projects. We also estimated on the order of
75-90% of our residential projects. We need to be up to the ridge on
the south facing roof for several reasons: a. limited roof space, so
that we are extending eave to roof, b. the higher on the roof, the
further from the edge and thus from shade impacts from surrounding
buildings and trees.
I would suggest looking at your own projects, and also a random
selection of pictures on the web of residential projects, and you will
see that many, if not most, are installed as high on the ridge as
possible.
Fire officials have not objected previously when there was access on
the other side of the ridge, but will most likely object if these
guidelines are adopted.
see:
http://osfm.fire.ca.gov/pdf/reports/solarphotovoltaicguideline.pdf
http://osfm.fire.ca.gov/training/pdf/Photovoltaics/pvinstallationguideliines.pdf
Powerpoint presentation. Of interest: almost every actual PV
installation (including the Marin Fire Station) appears to have PV
modules extending to the ridge. The one exception has a chimney at
the ridge, but modules on the rest of that installation extend to the
ridge.
http://osfm.fire.ca.gov/training/pdf/photovoltaics/solarphotovoltaicguidelinecover.pdf
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org