Hello

With the growth of the solar industry coupled with the generous incentives now 
offered on fed part of the equation, we are seeing some trends here and 
wondering what the approach has been in other areas. What kind of feedback are 
you receiving from the AHJ?

There are some integrators who now are installing "systems" meaning, multiple 
small inverters that are married to smaller arrays as opposed to one large 
array with one large inverter. 

So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters on a 
customers home. So, the point of connection issues arise. When you look at 
690.64B, it speaks to the 120% of the busbar rating.

What are folks doing in other areas, for this above example to address the 
mechanical/electrical challenges associated with this situation, when if you 
had 1- 200 amp residential service? There is alot of discussion, like 
installing a 125 amp rated subpanel; interuppting the feeder from the electric 
service and installing a 225 amp panel with a higher rated buss (hard to find 
or custom made thru Cutler Hammer or others) etc.

We can also see a trend using the enphase products as well, but not as much 
pronounced. It could be conceivable for a client to want to build their system 
up over a few years and have 15, 175 watt panels on a circuit (2P15 amp) and 
grow the system up to lets say, 45, 175 watt panels (3-2P15 amp). Same 
situation, different inverter manufacturer. My sense is this trend will 
continue for the forseeable future, and alot of wrenches will find orphaned 
systems out there and we should look at ways to address point of connection 
issues that are bound to present themselves.

Thanks

Keith



      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to