Hi Russ,

That is how I see it too. There are times that I shudder when we connect to an underground piping system, because as far as I can tell, the inspector could require a 4/0 GEC which would not only cost a fortune in copper, but pose technical difficulties.

Drake


At 08:14 PM 3/3/2009, you wrote:
Hi Drake,

The NEC says that "The size of the grounding electrode conductor for a dc system shall be as specified in 250.166(A) and (B), except as permitted by 250.166(C) through (E)."

The "except as permitted by" is what allows us to not run a 4/0 GEC.

250.166(C) says that the GEC doesn't have to be larger than #6 copper for connection to a rod, pipe, or plate electrode. (I don't think pipe-as-part-of-the-plumbing-system is what is meant by "pipe" there, since 250.52(A)(5) and (A)(7) are referenced, and 250.52(A)(1) deals separately with metal water pipes that come up from underground.)

250.166(D) says that the GEC doesn't have to be larger than #4 copper for connection to a concrete encased electrode.

No mention is made of the maximum size of GEC connected to the plumbing system in section 250.166, so the size of the GEC in that case might have to comply with (A) and be way larger than necessary.

That's how I see it, at least.

Russ

Russell Mueller
SolarRay Inc.
[email protected]



Drake Chamberlin wrote:
Hello Wrenches,

Revisiting the grounding requirements for DC systems, the grounding electrode conductor is still required to be as large as the "largest conductor supplied by the system" (250.166(B). When we run a GEC to a piping system, or the re bar cage embedded in the concrete foundation of a building, it still reads like we need to meet this requirement.

If the system is a 24 volt, battery connected, VFX 3524, it still seems that we would need to run a 4/0 GEC. Inspectors backed off making us do this a dozen years ago. Why are we not being required to do this now?

Thanks,


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to