Yes the electric power and atmospheric grounding systems should be connected 
together to serve as a larger better grounding system.  The Electrical code 
requires that at only one point does the neutral (grounded) conductor of the 
electrical power system get connected to the grounding system, this is to 
prevent the grounding electrode system from carrying electrical power system 
currents.  The electrical power system is to be grounded to prevent the 
electrical power system from differentiating its self via the injection of 
energy from other electric power sources including atmospheric electrical 
energy.    
 

The lightening protection system is to create a path from the atmospheric 
energy to the earth grounding system.  ((Wind rain, dust and friction cause the 
atmosphere to become charged relative to the earth, conducting objects can 
build a charge if not electrically connected to the earth, these current flow 
all the time, although they are small sometimes, and in the case of a 
lightening strike incredibly large.  Even small currents can build large 
voltages and fail electronic components.  

The frames of solar modules are electrical conduction components not normally 
charged that can present a personal, and physical damage potential 
(life-property) if they become charged by the electrical power system and 
therefor the underwriters require they be protected by grounding.  This 
accidental energy need to be safely returned to the electrical power system, 
and properly this is called bonding back to the neutral conductor.  This 
grounding is described by the NEC in 690 and 250 primarily.   The frames of the 
modules can become charged by atmospheric energy energy, this energy needs to 
be returned to the earth, via the lightening protection system, ie grounding 
electrode system.  The code says little about this, however, it is addressed in 
690 and 250.  

Sorry I said so much.
Darryl        


--- On Fri, 3/6/09, Drake Chamberlin <[email protected]> 
wrote:

> From: Drake Chamberlin <[email protected]>
> Subject: Re: [RE-wrenches] Lightning protection system
> To: "RE-wrenches" <[email protected]>
> Date: Friday, March 6, 2009, 8:47 AM
> I didn't get a reply to the question about connecting
> the GEC to the 
> lightning protection system on the 8 story building. 
> Although this 
> may seem like an intrinsically dangerous idea, a lightning
> protection 
> system is required to be bonded to the building grounding
> electrode system.
> 
> "250.106 Lightning Protection Systems.
> The lightning protection system ground terminals shall be
> bonded to 
> the building or structure grounding electrode system."
> 
> It would therefore seem that the suplemental ground could
> connect to 
> that system as well, and in fact use the existing
> conductor.  Any 
> input would be welcome.
> 
> Thanks,
> 
> Drake
> 
> 
> 
> 
> At 09:19 PM 3/4/2009, you wrote:
> >Hello Wrenches,
> >
> >Can the supplemental grounding electrode conductor be
> connected to a 
> >lightning protection system?
> >
> >We have a case where it would be difficult to run a GEC
> down a multi 
> >story building, but have a convenient copper wire, from
> a lightning 
> >protection system, that runs to a rod.
> >
> >Thank you,
> >
> >Drake Chamberlin
> >Athens Electric
> >OH License 44810
> >CO License 3773
> >740-448-7328
> >740-856-9648
> >
> >
> >_______________________________________________
> >List sponsored by Home Power magazine
> >
> >List Address: [email protected]
> >
> >Options & settings:
> >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> >List-Archive: 
> >http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> >List rules & etiquette:
> >www.re-wrenches.org/etiquette.htm
> >
> >Check out participant bios:
> >www.members.re-wrenches.org
> >
> 
> Drake Chamberlin
> Athens Electric
> OH License 44810
> CO License 3773
> 740-448-7328
> 740-856-9648  
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org



      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to