Jon:

1. Outback inverters are notorious for reporting errors incorrectly. Often the errors are a clue, but not the actual error. As an example, a shorted AC output might report a "Low Battery Voltage" error because when the output is shorted, the battery draw is momentarily very high, reducing it's voltage. Look for a related symptom.

Have you been able to monitor the AC voltage during inverter sell operation? High AC voltage in a grid-tie system can be caused by actual, intermittent high grid voltage and/or inadequate feeder size, allowing the inverter to push up the voltage at the inverter end of the feeder. I've seen a bad breaker cause this as well. In any of these described cases, the inverter error reporting would be accurate.

2. Outback sends out a standard kit of three field-replaceable boards. You rarely need to replace all of the boards. You need to figure out which board(s) to replace or, ask tech support. I guess when in doubt, one could replace all three. It appears you have narrowed the problem down to not one of the three boards.

Good luck.

William Miller




At 08:28 PM 4/9/2009, you wrote:
I have a customer with an Outback GTFX 3048 that has an"over voltage
AC in" warning but when I check the voltage with my Fluke meter it
shows a normal range 122 - 126 V . In the Mate grid menu the AC high
Volts is set at 140 V . The customer called Outback support before I
could get to him and they told him he needed to have me change all 3
boards out. They sent the boards so I went ahead and changed them
out, but the same error occurred again. We called Outback support
again but did not get a satisfactory answer on how to fix it.

Has anyone else run into this problem ? I suspect the Mate may be flaky.

Jon

Jon Haeme Innovations
Kempton, IL _______________________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to