Voltage drop and Vd%

 

We have been using a Calculated Industries  - Electro-Calc Pro for the last
3[?] Code changes.  Web site is   www.calculatedindustries.com

Conduit size, multiple combinations of wire size, Vd, Vd%, Ground size, HP,
you name it & it calculates it. The calculator has an upgradeable chip for
the changes in the code when that happens. Great investment @ $129??

It is all a few key strokes away.

We keep one on the desk, one in the travel case and on each truck.

. 

 

 

 

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - [email protected]

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

"I'd put my money on solar energy. I hope we don't have to wait 'til oil and
coal run out before we tackle that."

-Thomas Edison, in conversation with Henry Ford and Harvey Firestone, March
1931

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Drake
Chamberlin
Sent: Wednesday, April 22, 2009 8:15 AM
To: [email protected]; RE-wrenches
Subject: Re: [RE-wrenches] Long MC Cable Mid String

 

I have scratched my head on this one before, because it seems that two
terminals bonded together by a wire are essentially the same terminal.  The
theoretical voltage difference on a terminal is zero.  How do we figure a
voltage drop on a wire that has near zero volt potential between the ends of
the wire.  Can we really use the voltage of the entire array to figure the
drop on an interconnect between two modules?   If so, why can we do this?

Thanks,

Drake 



At 07:49 PM 4/21/2009, you wrote:



David,
There will be less than a 1 volt drop in 36 feet of 10 AWG at the 11 amps
you get from the Evergreen modules.  I don't think anyone will notice.
David

David Katz


David Palumbo wrote: 



Does the following series string wiring cause a problem? With  (18)
Evergreen ES-A 205's (low voltage modules 18.4Vmp) in series feeding a grid
tie inverter with a long series connector in the middle of the string.  (2)
Top Of Pole 9 module mounts with the series connection from module #8 on the
first pole to module #9 on the second pole. This MC cable connection would
be, about, 36 feet in length to go 10' down the pole below grade 18" for 13'
and back up the second pole 10' (in conduit all the way) .
 
Will this extra long series wire cause problems?
 
I could use other modules of course but that would raise the cost per watt
by 70 cents.
 
Dave
 
David Palumbo, President
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
NABCEP Certified
www.independentpowerllc.com 
 

 
 
 
 
 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to