HI Allan,
I would like to throw out that there are other options.
You could use timers with electric valves if you had some idea of how
much water each system might use, set a timer for each system.
Or you could use float valves with relays and electric valves to fill
each tank as needed.
Just depends on how important the water is.
jay
peltz power
On Jun 13, 2009, at 11:34 PM, Allan Sindelar wrote:
I agree with Brian and Mark on most of their comments, but here’s a
bit more:
Mark is right, there’s no way to separately control filling two
tanks at different levels. I didn’t read that section very
carefully. Brian’s float valve approach and sequential filling is
about the only approach. But given that a float valve failure could
be catastrophic (5,000 gallons flowing back down) you might want to
add a check valve on the line to the higher tank, if the line from
the well to the two tanks is shared.
Remember, too, that the total dynamic head is measured from the
water level in the well, not the pump level. That means your tdh on
the far well is something less than 220’, or about 97 psi (plus
friction head). Assuming you don’t have 3,000 feet of signal cable
in the ground, the P2Flow approach would likely work well. Their
0-100psi transducer has a resolution of 0.1 psi. Make sure to add a
check valve where the line leaves the well, so as to be unaffected
by fluctuations of the water level in the well, and put the pressure-
sensing transducer after the check valve, so that it only measures
head determined by the tank level. We’re working with a similar
application here in New Mexico, so I’m learning this too.
One respectful disagreement with Mark: The 3SQF-3 Grundfos is
officially rated to 656’. I hear it will do well more than that, but
no direct experience. I would not recommend the Lorentz after
multiple failures back when Dankoff (now Conergy) was the sole North
American distributor. (We are in Santa Fe so do will call pickups
for most orders. Don’t ask me to describe seeing pallets of junk
Lorentz pumps outside their warehouse, waiting to head to the
recycler.)
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
From: [email protected] [mailto:[email protected]
] On Behalf Of Brian Teitelbaum
Sent: Friday, June 12, 2009 2:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Design help for solar water pumping
application
Hi Lee,
I don’t know how the two tanks are laid out physically, but if they
happen to be installed in a way that you could run one pipeline up
to the tank at 200’ and go from there to the other tank, you might
try using a float valve in the lower tank and a float switch in the
upper tank. The lower tank’s inlet would just be “teed” off of the
pipeline going to the upper tank. The lower tank will fill first,
being the path of least resistance. When it is full, the float valve
closes sending water through the pipeline to the upper tank. When
the upper tank is full, the float switch would turn the pump off.
The distance to the float switch in the upper tank is a bit far, but
you should be OK if you use a larger gauge wire than usual. I think
that 18 gauge would be fine, but 16 gauge would be better. If it is
line-of-site, you might look into doing a wireless control , but
that would mean that you need a small PV module and a battery up
there.
Go with the 1 ½” pipe
Not to contradict Mark (Ok…I guess that I am!) The Grundfos model 3
SQF-3 will do 600’
As to Allen’s comment about array size, he is correct about the pump
drawing a max of 900W. However, if you only put a 900W array on the
pump, it will only pump at max volume at mid-day. If you put a
larger array on the pump, the array will produce 900W in less light
(morning and afternoon) and produce a lot more gallons per day
(GPD). The GPM figure of a solar pump is really only relevant for
making sure that you don’t over pump a low yielding well. It’s
really GPD that counts. That 1.36kW array might produce 900W at 9AM
and 3PM, giving you a solid six hours of max output pumping. No
problem over sizing the array – the pump will only draw what it
needs. If you have really good exposure to the sky, you can use a
tracker to increase GPD instead of over sizing the PV.
According to my info, with 250” of head (220’ plus pipe friction
loss) you can get about 2000 GPD (summer) with the Grundfos model 6
SQF-2 and about 700W of PV in a fixed array, with a peak flow of 4.5
GPM. Adding more PV will give you more GPD. With the model 11 SQF-2,
you can get up to about 4300 GPD with a 1750W array at that head. If
you needed even more water volume, and the well produced it, you
could even put two pumps in the well (with separate arrays). I had
one dealer who managed to put two Grundfos pumps down a 5” casing!
He said that it all went easy….but I don’t believe him. He did have
a curious issue though. He said that if he turned one pump off with
its CU200, both pumps would shut down, even though the other pump
was not connected to that CU200. He couldn’t just run one pump. I
never did talk to Grundfos about that.
Cheers!
Brian Teitelbaum
AEE Solar
From: [email protected] [mailto:[email protected]
] On Behalf Of Mark Dickson
Sent: Thursday, June 11, 2009 9:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Design help for solar water pumping
application
Hey Lee,
Allan is right in that the WINcaps software is a lifesaver and
FREE! Not to contradict Allan, but I do not see a feasible way of
using two float switches in separate tanks with only one pump
controller. Also, the 3000’ distance is a little far—they usually
recommend a max distance of 1600’ for the float switches. Lastly,
if you are ever worried about the head, the Lorentz pumps can pump
up to 760’ --more than double the recommended for Grundfos.
I highly recommend Genpro Energy Solutions as a pump distributor for
both of those brands. They always answer the phone, are personable
and return emails (hint, hint Conergy)!
Best,
Mark Dickson
Oasis Montana Inc.
www.oasismontana.com
www.grid-tie.com
www.PVsolarpumps.com
From: [email protected] [mailto:[email protected]
] On Behalf Of Allan Sindelar
Sent: Thursday, June 11, 2009 2:28 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Design help for solar water pumping
application
Lee,
You can get Grundfos’ WINCaps software from your RE or pump
supplier; some will run the sizing for you (Jeremy at Conergy does
for us). I didn’t check your head and flow, but I would expect
that’s about your only good pump choice at that head. Add a tracker
if you need greater summer output; don’t attempt batteries as a
solution. If usage occasionally exceeds output, add an IO101 control
and allow the pump to run off any AC source at night. A tiny 1,200W
inverter/generator will work at sea level. Use a CU200 controller to
allow a float or level detector switch to turn off the pump when
tanks are full. Mercury-based float switches last longer in signal
circuits that carry no current. If you can’t use a float switch
because the lines are already buried, look intowww.P2Flow.com for
pressure transducer-based control. Read the website info, then call
Britt there with your specific application. That array sounds
oversized, as the pump draws a maximum of 900 watts. Hope this helps.
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
From: [email protected] [mailto:[email protected]
] On Behalf Of Lee Bristol
Sent: Thursday, June 11, 2009 1:26 PM
To: [email protected]
Subject: [RE-wrenches] Design help for solar water pumping application
Solar Water Pumping Wrenches,
We normally don't do solar water pumping but a friend asked for some
help designing his system. He has one well and two 5,000 gallon
reservoirs to fill up. The average usage is expected to be about
2,000 gallons per day but may be higher in the summer. The tanks
will have level detector switches to sense when the tank is full.
The site is near Leesburg, VA.
The problem is to design a control system to turn on the pump when
one or both of the tanks needs water and to shut it off when both
are full. The closest tank has a head requirement of 200 feet (pump
to tank) and is 300 feet from the well head. The second tank head
requirement is 220 feet and it is 3,000 feet from the well. The
pipes are expected to be 1.25 or 1.5 inch.
A Grundfos SQFlex 6 SQF-2 pump with 1.36 KW solar was recommended,
360 foot head, 360 gph. I think that this would provide the lift
but not the quantity. Hmmmm, what valves and controls would you all
suggest?
Thanks!
Lee
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org