Don,
SolarMagic is an MPPT DC to DC converter that you put on every modules in a string where some of the modules are going to be shaded. You would only do this if there are other strings that had no shading. When a module (or two) in the string is (are) shaded, the SolarMagic devices on the modules that are _*not*_ shaded raise their output voltage and lower their current, keeping them individually at maximum power point so that this string has the same voltage as the non-shaded strings in the system, and is therefor matched the MPPT voltage of the string inverter. Typically, if you shade a module in a string, its voltage drops somewhere between 1/2 of its peak power voltage and all of its peak power voltage. This can lower the string 20 to 40 volts. If there are other non-shaded strings attached to the input of the same string inverter, the shaded string will try to rise in voltage to equal the non-shaded strings, causing the modules in the shaded string to each rise in voltage several volts, taking them off their maximum power point. Because of the nature of the I-V curve of the modules, this may lower their output by 25% to 50%, lowering the power of that string bu more than 25%-50%. SolarMagic would cause the string to only drop by the wattage of the shaded module, possible only 5% in a 20 module string. I see the use of these devices making sense as a retrofit in a system that was installed by someone who did not understand how much loss there is in a shaded string that is in parallel with non-shaded strings.
Cheers,
David

David Katz

President

AEE Solar

1155 Redway Drive

P.O. Box 339

Redway, CA  95560

Tel (707) 825-1200

Fax (707) 825-1202

[email protected] <mailto:[email protected]>

www.aeesolar.com <http://www.aeesolar.com>


Ok, so I've read the pitch from the Manu, however not sure even if the published specs for shade improvement are very convincing to me..
Would one of my esteemed colleagues explain what it does and how it works.
Thanks, Don Loweburg
------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to