Troy,

Unless you are going to be your client's power plant manager, he or she is 
going to have to be responsible for at least system operation which means 
managing production and consumption - or hire someone to manage the system. PV 
systems are automatic and virtually maintenance-free to some extent. A 
well-designed, properly installed batteryless grid-tie residential PV system's 
operation is transparent to the home occupants and requires very little 
attention. However, a battery-based system regularly requires operator 
intervention especially in a region with frequent brown-outs and black-outs. 
There are several Wrenches who live with battery-based grid-tied PV systems. Do 
any of you power your whole house through the main service panel (no subpanel)? 
If yes, what size PV array, inverter, and battery bank? Any battery-based, 
grid-tied PV systems out there in continuous operation since before June 1998?

Joel Davidson
  ----- Original Message ----- 
  From: R. Walters 
  To: RE-wrenches 
  Sent: Tuesday, June 23, 2009 10:29 PM
  Subject: Re: [RE-wrenches] Grid-Connect Inverter with battery,AND auto 
backoff?


  We've looked at a variety of approaches over the years. My current thinking, 
is that you want some non critical loads to shut off during an outage, so the 
customer knows they are on backup power. With whole house backup, they never 
know till the batteries are gone too. I've found that with creative picking of 
circuits, the customer can be signaled that the grid is out, without creating 
any panic or hardship. Most houses have so many circuits that its just not a 
big deal to have the washing machine not work for a few hours. 
  I'd back off to a proven design, otherwise your going to spend a lot of time 
with them making this work. Manually switchable double throw breakers are 
available and work well, but yes, you do have to exert some slight mental and 
physical effort to operate them. Automatic anything means the installer is 
always to blame. Good system design puts some responsibility on the operator as 
well.


  R. Walters
  Solarray.com
  NABCEP # 04170442 






  On Jun 23, 2009, at 10:30 PM, Troy Harvey wrote:


    Load sheding is not a bad idea if the tech exists. Not particularly complex 
either with networkable breakers and a smart controller in the inverter. Just 
software. Cost isn't an issue, they are willing to pay.


    The issue on loads isn't battery cut-off (though that isn't a bad idea), 
but shedding the less-important loads to make sure the house does exceed the 
inverter power output. A 6kW inverter subpaneled will only give you about four 
15 AMP circuits. However a typical house of this size will have 30 such 
circuits, yet good chance it won't be drawing much more than 50 AMPs for the 
whole house at any one time. How do you select what is important? Either the 
inverter is complicated or the electricians wiring is complicated.




    Troy Harvey
    ---------------------
    Heliocentric
    801-453-9434
    [email protected]




    On Jun 23, 2009, at 10:01 PM, William Miller wrote:


      Troy:

      Let me guess... They want it right away and cheap, too.  Generally 
speaking, this is an impractical request.  Electrically operated circuit 
breakers or 20 A relays and controllers are expensive and complicated.  One 
thing to learn in this trade is when to try and talk a client out of a bad 
idea, and when a client has such wacky ideas that it is best to walk away.

      I could, however, suggest two ways to do this:

      1. Use two inverters and set the LBCO for one high.  Connect one to 
critical loads and one (with the high LBCO) to non-critical loads.  When the 
batteries start getting low, the non-critical-loads inverter shuts down, 
leaving the critical-loads inverter running.

      Realize that you now need four load centers:  Grid, generator (you have 
recommended a generator so they can use their wide screen TV during a wind 
storm, correct?), non-critical loads and critical loads.  This type of design 
gets complicated fast.  Will the AHJ be able to track this?  Set a clause that 
allows you to collect hourly fees when they require three different meetings 
and three re-writes of the permit application.

      2. Use an Outback with external relays to shut off loads when the battery 
voltage falls below a certain point.   This is a crude approach, the parameters 
are not flexible (hard coded delay values) and it requires custom built relay 
panels, time consuming, expensive and a potential service problem.

      Either system is actuated on battery voltage rather than loads.  
Inverters I am familiar with have relays and internal controls that operate 
based a set-able battery voltages, but I know of none that has a programmable 
relay to actuate at a certain load level.  In addition, loads change so rapidly 
that this type of switching would be erratic.  Loading is a component of 
battery voltage, anyway, so you are including that indirectly.

      Good Luck,

      William Miller



      At 07:41 PM 6/23/2009, you wrote:

        Hi folks,

        I need an inverter/charger/controller solution for a grid connect  
        house that:
        1. grid-connects (net-meters)
        2. Islands off of the battery in outages (whole house UPS)
        3. Feeds into the whole house breaker, so the whole house is backed up
        4. Shuts down less important breakers as needed, if the load for the  
        whole house is over the inverter limit

        Instead of guessing which breakers are important to put on a battery  
        backed up sub-panel, my client would like the whole house backed up.  
        But of course, can't guarantee that the house won't be drawing too  
        much for a 6000 Watt inverter at any given time. So would like to have  
        the system intelligently remove less important breakers until the  
        system is below the inverter operation wattage.

        Anyone know of a inverter system that is smart like that?

        Troy Harvey
        ---------------------
        Heliocentric
        801-453-9434
        [email protected]
      _______________________________________________
      List sponsored by Home Power magazine

      List Address: [email protected]

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org




    _______________________________________________
    List sponsored by Home Power magazine


    List Address: [email protected]


    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm


    Check out participant bios:
    www.members.re-wrenches.org






------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to