Wrenches,

 

Point of information.we have been using a Honda EM7000is for 5 years with
dual SW4024s in an off grid system with absolutely no issues.  We leave the
"eco throttle" in the "ON" position and have experienced no sync, load
sharing or battery charging issues regardless of load.  Our largest single
load is a 220V 2HP well pump set at approx 400'.  The generator and
inverters handle it with no problems.  

 

John Ollson 

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Brooks
Sent: Wednesday, July 15, 2009 6:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] FW: Backup Generators

 

Allan,

 

Does the Honda have a "eco-throttle" setting that throttles back under light
load?  If so, turn it off so the inverter sees full voltage and frequency
and can sync with no other loads on.

 

Randy Brooks

Brooks Solar, Inc.

Solar Power for People

140 Columbia View

Chelan, WA  98816

509-682-9646

[email protected]

www.BrooksSolar.com

 

On Jul 14, 2009, at 11:24 PM, Allan Sindelar wrote:





Wrenches,

This man wrote me about a generator/inverter compatibility problem he's
having. I haven't heard of it before. I suspect it's more than just a simple
voltage-frequency issue, but I haven't heard of this or experienced it. Any
ideas?

Thank you, Allan Sindelar

 

In the Spring of 08, I purchased a Honda EU6500is generator as a back-up to
my off grid solar system.  The Honda was to replace my Yamaha YG6600DE
generator which worked fine with my Trace SW4024 inverter.  However the new
Honda inverter-generator seemed to have problems working with my Trace
inverter.  If I had a load running, such as my 110 V well pump, it would
handle that load and the excess power from the generator was used to charge
the batteries through the Trace 4024.  But once the well pump shut off, the
Honda generator and the Trace didn't seem to like to work together.  The
Trace inverter stopped allowing the incoming power to be used to continue to
charge the batteries by disconnecting AC2 power (generator) from coming into
the SW4024.  After replacing the Honda with the old Yamaha generator,
everything worked fine again, including charging the batteries without
another load on the inverter.

As a result of the above, my question is:  Have you experienced similar
incompatibility with inverter-generators and inverters such as my Trace
SW4024?    If so, do you have any suggestions that will allow me to use my
Honda EU6500is with my Trace 4024?  Calls to Xantrex and Honda on this issue
did not provide any useful information.

Thank you, Michael 

 

_______________________________________________

List sponsored by Home Power magazine

 

List Address: [email protected]

 

Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

 

Check out participant bios:

www.members.re-wrenches.org

 

 

Checked by AVG - www.avg.com
Version: 8.5.375 / Virus Database: 270.13.14/2238 - Release Date: 07/14/09
18:03:00

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to