boB,

The Mitsubishi system is just two parallel strings. The combiner was planned for future expansion. It was last fall that I had trouble with those so I don't remember if they were "off" or "tripped". The system with Evergreen panels is just three strings; it is possible but not likely that the problem is a fault in the array. I found that breaker in the "off" position. And that is strange, because it is really unlikely that anyone has been in the combiner box during the last year.

Kent


boB Gudgel wrote:
Kent Osterberg wrote:
Allan,

I've had trouble with breakers opening when they shouldn't. On an array of two strings of Mitsubishi 175s (Isc = 7.9A) I had two 15-A breakers open. Last week, I had a low-power call from a customer with three strings of Evergreen 190s (Isc = 7.1A); one 15-A breaker in the combiner was open. Most of my installs are around 3000 ft elevation, so the irradiance is possibly a little higher than normal, but not by enough that it should be an issue for 15-amp breakers. If this is a wide-spread problem, I'd expect others on this list to have noticed.

Hi Kent,

Could there be a defective module and the breaker is just doing what it is supposed to do ?? What is the series fuse rating for those modules ? (probably 15A?) A shorted or defective module would cause those other strings to make it trip, if there are enough parallel strings. I hope there isn't some kind of intermittent problem...

Was the breaker actually in the "tripped" position or the "off" position, since there is a difference? (tripped of course means
that there is some play in the lever.)

We (and OB) have sold literally over a million (or millions?) of these breakers and we just haven't seen any problems. You have been using these breakers for years now... Have you seen problems before this ?? I understand that any problems with CBI breakers have been AC breakers, not DC, and even then, problems have been far and few between.

You could test the breakers though... Just shove, say, 10 Amps through one of the questionable breakers and see if it trips after a while.

It seems kind of odd that more than one of these breakers would have defectively tripped near the same time ( week ? day? week-day?).

There is, I suppose, the possibility that they could all of a sudden have started having some kind of problem, but CBI breakers have had an excellent track record for many years now. We haven't heard anything from any other customers here at MidNite.

Can't wait to hear what's causing this problem though... I'm sure it will be very interesting !

boB




As others have mentioned, it is important to take precautions to make sure that stranded wires are well tightened in these breakers. I tighten, wiggle, re-tighten, and then check again later. On systems where I've had breakers open, loose connections haven't been the issue.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemoutainsolar.com <http://www.bluemoutainsolar.com/>


Allan Sindelar wrote:
I have had no problems to date, Kent. Can you be more specific as to what
problems you have had?
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

-----Original Message-----
Is it just me, or have other wrenches had problems with the CBI circuit breakers used in the Outback or Midnite combiner boxes?

Kent Osterberg
Blue Mountain Solar, Inc.
http://www.bluemountainsolar.com/
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org