Hey Darryl,

You said - " never allow a single wire to pass through a metal surface as this 
will induce eddy currents and magnetic effects into the metal causing voltage 
drop and heating"

Is that true even for non-ferrous metals, like aluminum, or say, gold?

Brian Teitelbaum
AEE Solar



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Darryl Thayer
Sent: Monday, August 03, 2009 1:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] solid vs stranded AC vs DC


I looked in the code book and found stranded wire has about 2% higher DC 
resistance than solid, Chapter 9 table 8, and that for AC resistance the same 
value as DC resistance to within the table accuracy Chapter 9 Table 9

This table points out that for AC resistance it is important to know the 
conduit system, as the reactance will have an effect.  With AC it is important 
to never allow a single wire to pass through a metal surface as this will 
induce eddy currents and magnetic effects into the metal causing voltage drop 
and heating.

--- On Fri, 7/31/09, jay peltz <[email protected]> wrote:

> From: jay peltz <[email protected]>
> Subject: Re: [RE-wrenches] solid vs stranded  AC vs DC
> To: "RE-wrenches" <[email protected]>
> Date: Friday, July 31, 2009, 10:01 PM
> Hi Darryl,
>
> But what are the differences and when do they come into
> play?
>
>
>
>
> On Jul 31, 2009, at 7:25 PM, Darryl Thayer wrote:
>
> >
> > Well there is very slight differences between AC and
> Dc But this
> > difference
> > is so slight that it has no effect on anything we will
> do.
> > Darryl
> > --- On Fri, 7/31/09, jay peltz <[email protected]>
> wrote:
> >
> >> From: jay peltz <[email protected]>
> >> Subject: [RE-wrenches] solid vs stranded  AC
> vs DC
> >> To: "RE-wrenches" <[email protected]>
> >> Date: Friday, July 31, 2009, 7:00 PM
> >> HI All,
> >>
> >> I'm trying to understand this wire issue.
> >>
> >> Whether or not there is a difference between
> stranded or
> >> solid wire for DC or AC.
> >>
> >> Any takers on this one?
> >>
> >> thanks,
> >>
> >> jay
> >>
> >> peltz power
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: [email protected]
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: 
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: [email protected]
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to