To All,
 
Thank you for the advise, experiences, and input. I apologize for the delay in 
my response, but my priorities have been temporarily changed for me, and moved 
away from this project.
 
First of all, yes we have made allowances to accommodate the 3 foot perimeter 
for egress access way for the Fire Department, and it would not make a 
difference if we separated the array with courses of non PV tile, as they are 
pretty set on their "Quick Release" requirement.
 
The installing electrician for the project has been dealing with the planning 
and fire departments directly in an effort to resolve the issue. The only 
printed reference to this requirement that I have received came from the 
corrections list from the Fire Department. (Chula Vista requires separate plan 
reviews by 1) Planning 2) Engineering and 3) Fire Department)
 
The correction list states "Hardware shall be of the quick release type - 
subject to Fire Department approval. The panels should be releasable from the 
mounting with the use of a gloved hand, and without the use of tools."
 
I am e-mailing Fire Prevention Engineer directly to request a published 
document for this requirement, but I really do not see how we will be able to 
satisfy this requirement, and will most likely loose the job. Our electrician 
will be meeting with them directly to see what if anything can be done. I would 
think that with a gloved hand they should be able to break and remove the tile 
just as they would with a concrete tile, with out the use of a tool.
 
I yearn for the day of a Nationally approved standard that ALL building 
officials will have to adhere to. As you are all no doubt aware, two 
neighboring cities might as well be on different planets when it comes down to 
how they review and approve PV Installations.
 
I actually just had a different planning department approve a set of plans that 
I produced that had two PV Powered 4800 Watt inverters (23A Max Continuous AC 
Output) with 30A breakers and a 400A Main Panel called out. It turns out that 
the customer only had a 200A panel, so the inspector told the installer that he 
could just reduce the size of the breakers to a 20A, the installer did this, 
and the job was signed off and finaled. The customer then had problems getting 
his rebate because the drawings still call out a 400A panel. I provided 4 
different options to rectify the issue and still meet code, but they do not 
want to do this. Now they are mad at me because I refuse to change the drawings 
to represent a non code compliant installation.
 
Part of me is amazed that the inspector and planning department has aloud this 
to happen, and the other half is not surprised at all.
 
I will update the list when I have more, and thanks again for the help.
 
Brian C. White
Sr. Design Engineer - PV Systems
 
Eagle Roofing Products
120 North Auburn Street - Suite 212
Grass Valley, CA  95945
Phone: 530-273-2948
Cell: 530-575-5550
e-mail: [email protected] <mailto:[email protected]> 
 
 

________________________________

From: [email protected] on behalf of Joel Davidson
Sent: Thu 7/30/2009 10:31 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] "Quick Release" PV System



Quick-release started with the Los Angeles Fire Department. The PV industry
rejected quick-release as impractical, costly, an invitation for theft,
etc., but it won't go away. For lots of background info on fire safety
requirements, see http://osfm.fire.ca.gov/training/photovoltaics.php


----- Original Message -----
From: "Brian White" <[email protected]>
To: "RE-wrenches" <[email protected]>
Sent: Wednesday, July 29, 2009 11:18 AM
Subject: [RE-wrenches] "Quick Release" PV System


"Quick Release" PV System

I just had a set of plans rejected by the City of Chula Vista, CA, because
the integrated Tile product that we use did not have a "Quick Release"
System for the array, so that the Fire Department could remove the array in
the event of a fire.

Has anyone ever heard of such a requirement? If so, how did you meet this
requirement, with any style of PV array (BIPV, Standard Modules, peel &
stick) and still achieve an 85 - 100 mph wind rating? Is it just me, or is
this city from a different planet.

This issue did not show up on the initial Plan Correction check list from
the city, but they are calling it out now when we re-submitted. My
electrician asked them to explain it to me over the phone, because he did
not think anyone would believe him when he asked for this requirement. I
have asked for a document or anything that defines this requirement, and
will share what I find out.

Brian C. White
Sr. Design Engineer - PV Systems

Eagle Roofing Products
120 North Auburn Street - Suite 212
Grass Valley, CA  95945
Phone: 530-273-2948
Cell: 530-575-5550



--------------------------------------------------------------------------------


> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



<<winmail.dat>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to