I'm beginning to wonder if the allowed voltage range for grid-tie inverters (+/-10%) is too sensitive in some networks and contributes more harm than benefit. This is close to home.

We actually have a significant number of customers who've had trouble with grid voltage causing their systems to go offline at various times. I think most or all are SCE customers.

So I've been having problems with the inverter at my own house going offline due to high utility line voltage. We actually have 4 other systems in the neighborhood, with two more going in in the next couple months. All of them are about equally affected, even though each house is feed by a different transformer. I did a bit of research and found that some of the grid hardware in the neighborhood is very old---some of the oldest in existence--- dating back as far as 1892. You can read about the San Antonio Power Plant (hydro)
and the Pomona substation online.

Going back to the 1950's, most of the local neighborhood sub- transmission in the US is at a voltage around 12 kV or more, with transformers for the 120/208/240 or 277/480. But some older neighborhoods that haven't been upgraded (and some campuses) use an intermediate system, usually 2400/4160 volts. My neighborhood is still mostly fed by
the old 2400/4160v network.

Generally, the utility voltage at my house is in the mid 120's--- around 125 vac per phase. But at times, the voltage goes up higher---two weeks ago I saw 129 to 130V per phase. That voltage was high enough to put all of the inverters that I checked offline for much
of the day.

So I've had to call in "voltage trouble" complaints to the utility at least a dozen times over the past 5 years in response to seeing inverters offline and line voltage about
8% above nominal.

This periodic voltage problem has been going on for years, typically worst in summer. I upgraded with new service panels and heavier feeders at each of the houses to do my part to help. The circuits are now sized so that voltage drop in every case from the inverter terminals to the utility entrances are all under 1% at full solar output. Six months ago, utility crews replaced some transformers around the neighborhood (some appeared to be original), yet they didn't move any customers from the old 4kV
supply to the newer 12 kV supply.

I've read that the utility's operating guidelines call for keeping the supply voltage
within +/- 5% of nominal voltage at the customer's service terminals.

If the utility actually stays within 5%, and if solar inverters allow for voltages to vary up to +/- 10% from nominal, then things _should_ be okay. However, in practice, I see the inverters going offline right at 129 to 130V per phase, not 132V (+10%).

In response to the last trouble call, I talked with the crew that came out. I think their response helps explain the problem... my issue seems to go back to the substation. Apparently other customers on another feeder from the same substation complain
about low voltage---around 108-110V per phase. So they raise the voltage
regulator at the substation and everyone goes up 5%. It's easy to see how the drop on a 4kV feeder could be 1% on one feeder and 10% on another---- example: a load of 865 kW (~400 homes with A/C) or 120 amps at 4kV 3 ph, in 2 miles of #2 copper is a voltage drop of 10%... yet 300 kW going 3000 ft gives a voltage drop under 1%. If voltage drop is 10% on one feeder, but only 1% on a different feeder... it's tricky for the operator to keep everyone reliably within 5% of nominal. In my neighborhood, SCE technicians apparently view it as normal operating
procedure to supply 126 or 129 volts per phase.

So it seems there are several possible remedies:
1) ignore the problem and hope I don't lose too many kWh's due to grid overvoltage

2) I could install transformers to lower the voltage to the inverters by ~5%----so far, grid voltage in my neighborhood has *always* measured at or above nominal.

3) if it weren't for the UL and IEEE standards, solar inverters could be set with values that made them compatible with prevailing utility operating conditions, perhaps
+/- 15% of nominal voltage.

4) at a cost of many millions of $$$, SCE could completely replace the local distribution system with new 12kV facilities, even though annual load growth
on the old wires is trivial or possibly negative...

5) at a more modest cost, SCE could make strategic upgrades to lower the load
and voltage drop on the most stressed parts of the old network


How have other installers dealt with utility voltage problems?

/wk

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org