Don:

The DC feeder may have an AC component imposed on it by the switching in the inverter. We installed a large Hawker battery bank (http://millersolar.com/Portfolio/Commercial/Cal_Trans/cal_trans_gorda.html) that physically vibrates under heavy charging. We have also seen in this forum reports of RF interference from battery cables.

William Miller



At 06:07 PM 8/19/2009, you wrote:
In a message dated 8/19/2009 2:42:48 P.M. Pacific Daylight Time, [email protected] writes:
1. Running the positive and negative wires through separate conduit
violates 300.3, and could cause eddy currents in the combiner/disc boxes.


No eddy currents with DC-- But not sure why all not run in single conduit.

Don Loweburg