Brian Teitelbaum wrote:
boB,
Not only does that make sense, it's the best explanation of the effect of power
factor on an off-grid system that I've read.
I would than assume that this means that Drake's refrigerator is actually consuming more
power from his battery system than is just measured in AC watts at the fridge. Some
energy is lost as heat in the inverter system while the fridge is running, at least more
than would be if the fridge had a higher power factor. I would also assume that measuring
the DC amperage in the battery cables, and subtracting the "normal" inverter
losses, would give a more accurate reading of the Fridge's true running watts.
There are a number of plug-in products on the market that are supposed to
improve power factor, apparently through added capacitance. How would they work
here, or would they?
Great question and I'm not sure I have a good answer.
You would have to modify the refrigerator itself to make it have a
higher power factor, and I would hope that the appliance manufacturer
has designed it to work as
good as it can. Are those high efficiency refrigerators power factor
corrected though, since Europe requires power factor close to 1.0 and
the good ones
are also used there ?
I've seen many discussions about those power factor correction units for
home use, and I think the consensus is that they really don't help much,
if at all....
...Mainly because the homeowner only pays for real power.
I think that the higher the inverter efficiency, the better it will work
with lower PF loads, because it has to keep its AC source impedance low when
powering that refrigerator (or whatever), because it has to circulate
and "slosh" around those reactive currents.
Lower resistance =equals= higher efficiency, =equals= better low
power factor performance, is one way to look at that.
Adding extra and opposite reactance for power factor correction is
something that utilities do at large reactive consumers such as steel
mills. It makes sense for that
type of power usage. BTW, if the primary power factor is low because
of big inductive loads, they add capacitors, and if capacitive, they add
inductors to pull the power
factor back towards 1.0. At least that's the "passive" method that I'm
familiar with for low Displacement Power Factor, (DPF).
But what happens if you have all that passive PF correction in place,
and all of a sudden the load reduces or goes resistive ? Then you're left
with a nice low power factor load again. (I think they take that into
account and make it average out).
Then, there's active, electronic PFC. I probably won't be around to
see, but I bet that high temperature
superconductors will play a big roll in reducing all losses.
boB
Brian Teitelbaum
AEE Solar
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of boB Gudgel
Sent: Wednesday, August 19, 2009 9:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] power factor
Drake Chamberlin wrote:
One question about power factor:
We know it is the ratio of the real power to the apparent power, and
that most utility meters only register real power (watts). Reactive
power doesn't dissipate as heat like power loss through a resistor.
The question is: What is the quantitative effect that reactive power
has on a battery bank that is feeding loads through an inverter? If
the power factor is 56% (like a refrigerator that I want to replace)
does that mean that only 56% of the power being drawn from the
batteries is being used to power the refrigerator?. If so, where does
the rest of the power go?
If you just take your meter and multiply Volts X Amps, that's VA, or
apparent power. If it's all real, then it's like the resistor and gets
counted by
the utility meter. Some turns into heat (resistor) and some gets some
real work done.
The rest, is VA but is Reactive and is VA Reactive or VARs.
So, the reactive current that comes out of the batteries, into the
inverter out the AC output, comes BACK into the battery. (this is for
an inverter
that has the ripple reflecting back into the battery)
So, your batter kind of discharges and then recharges 120 times per
second for a 60 Hz system.
So, where does the power go ? The real power gets used of course and
most of the rest, the VARs gets put back into
the battery. HOWEVER, since the transformer and wire and FETs and
transormer and stuff have resistance, some of those VARS get turned
into heat by that inefficiency, or I-squared-R losses. That's one
reason why low power factor isn't so good.
Does that kind of make sense ?
boB
Thanks,
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org