Hello All,

Have a question on a Magnum 1212MM-AE. The battery charger will not get above 13.8 Volts. The system worked fine for the first three weeks with Voltage rising to 14.4 volts for the absorb cycle, but now it will not. The battery size and type setting are correct, and using the "custom" charging profile set to 15 Volts does not work.

We have tried unplugging the BTS, while also making sure the battery Voltage is below 12.7 when starting the generator. The remote control is attached and there is 35 amps going into the battery with a 2KW honda. It will sit at 13.8 Volts and do an absorb cycle for 2 hours and then go into float. There are 4 golf cart batteries in the system and all cells check out good, no dead cells, and connection are all bright and tight. Turning the main DC disconnect off while the gen is running shows 14.8 Volts at the battery terminals of the inverter, but the batteries will not rise above 13.8. Magnum says the battery charger is fine since it goes up to 14.8 when the batteries are disconnected, but that doesn't make for a very efficient charger if it is not connected to the batteries......

I am not familiar with these chargers, did I miss something, any ideas?