Bill and all -

Good old home depot. Are these bushings you speak of similar to the one 
pictured here?

http://www.amazon.com/gp/offer-listing/B000UEDU6M/ref=asc_df_B000UEDU6M915738?ie=UTF8&condition=new&tag=dealtmp386263-20&creative=380345&creativeASIN=B000UEDU6M&linkCode=asm

If so, I'm wondering if these are rated for outdoor use. I found one link that 
seems to mention that they are indeed rated for indoor and outdoor use but that 
would surprise me since the lay in lug is made of aluminum and I don't think 
the screws are stainless. I thought only tin coated copper lugs with stainless 
hardware are good for outdoors.

My other question is if we run, for example, a #10 bare copper ground through 
this lug and then into the EMT is it ok to have the bare copper touch the metal 
conduit? As I mentioned on a previous post it doesn't seem like a good idea 
from a galvanic perspective but through experience I haven't found any problems 
with it. Does any one have any reference to code material specifically allowing 
or not allowing this?

-August

August Goers

Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167

From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Friday, October 09, 2009 2:55 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

August,

Home Depot now sells bonding bushings for EMT down to ½", which should solve 
the availability issue. I was very surprised to see them last trip to the HD 
money pit.

Bill.
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org