Hi Kent,

We're trying to work the bugs out of our first FNDC for a demanding customer. It came as part of a DC Power assembled power center. They had added a circuit of their own design that had an Auto-Off-Manual toggle switch and a relay that was connected to both the FNDC and the FX aux. It didn't work. Outback said to use either the FNDC relay or the FX aux with an external relay, which is what we did, and it's worked fine for several months, controlling the generator by SOC. However, lately the SOC reading seems to have gotten out of sync with reality, big surprise. The volt start settings are over-riding the SOC. The challenge is how to camp out at the customer's house for a week to make the observations and tweaks to get all the programming set up appropriately to the realities of the battery and array.

I would suggest removing generator control from the FNDC relay and let the Mate/AGS control an external relay. The FNDC seems to feed it's data to Mate so it can work off of SOC.

I agree with others that the FNDC screens are way too complicated for all but a tech-head customer. At least the Trimetric is simple enough you can get almost anyone to read amps and volts, and even, God forbid, days since charged.

Bruce Erickson
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701



On Oct 15, 2009, at 9:35 AM, Kent Osterberg wrote:

Wrenches,

I see there are lots of negative feelings about the FNDC and about how complicated the Mate is in general. I haven't seen many direct responses to the question. Have any of you used the relay in the FNDC and had problems with it not turning the generator off?



Kent Osterberg wrote:

Has anyone besides me had problems using the relay in the Outback FNDC? I've had three different customers report that their generators failed to turn off.

--
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.421 / Virus Database: 270.14.16/2435 - Release Date: 10/14/09 06:33:00


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to