Holt,

I see that nobody has jumped in to respond to your question, so I guess that I 
will.

I don't know of any "off-the-shelf" monitoring system that would directly 
integrate the two systems. Fat Spaniel Technologies might be able to put 
together a combined system, but it would likely be expensive and complex.

However, the vast majority of the time the SB6000 would just be in standard 
grid-tie mode, so you can just use the SMA WebBox and Sunny Portal to monitor 
the SB. Even if the grid is down, the SB output could be monitored. It just 
wouldn't tell you where the energy is going - to run loads or to charge 
batteries. But do you really need to monitor that?

Most of the time the OutBack will be doing nothing but waiting for a grid 
failure, but If you want to also monitor that inverter, you can use the FLEXnet 
DC and the MATE to connect to a PC.  Right Hand Engineering makes nice 
Windows-based PC software that works with the OutBack equipment to monitor and 
display status, with data logging and system control:

http://www.righthandeng.com/hm_wvmob.htm

Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, October 20, 2009 6:45 AM
To: RE-wrenches
Subject: [RE-wrenches] Monitoring split system

Have residential grid-tie system as follows: 6kw direct grid-tie w/SB6000, 2kw 
battery base back-up w/OutbackGT3648.  Been waiting for Sunny Beam, have kwh 
meter on OB - Any way to coalesce the two into single monitoring station? 
Web-based prefered.
Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco TX. 76712
254-751-9111
www.holteksolar.com<http://www.holteksolar.com>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to