Just a note here- rather than using the record lows, you can go back to the future and use the ASHRAE minimum expected temperatures as the 2011 NEC will allow explicitly. In the '08, it says to use the "lowest expected ambient temperature," for which the ASHRAE temperatures are more appropriate than record lows. These ASHRAE temps will be higher than the record lows and will add a little more cushion there at 600 VDC.

So where to get these temperatures? Starting on page 47:
http://www.solarabcs.org/permitting/Expermitprocess.pdf

Also, in case you didn't know, www.pvselect.com is another option for string sizing that features multiple inverters and a 1 degree temperature step rather than the 9 degree (F) temperature step on the SMA sizer. They have the Kyocera KD130 in their database, but not the KC130.

DKC

-------- Original Message --------
Subject: Re: [RE-wrenches] SWR2500U Inverter
From: Brian Teitelbaum <[email protected]>
To: RE-wrenches <[email protected]>
Date: 2009/11/18 01:34

Joel,
The SMA SWR2500U inverter has been a long discontinued model. If you want to use an SMA inverter, go to the SMA website to use their excellent sizing program. Plug in the module, and your record minimum and average maximum temps for the site, and look for a current model inverter that will work. All of the "U" series inverters (except for the 700U) are discontinued models, and the "US" series are the current models. If your min temp is not below 14⁰F, it looks like you can use all 24 in one series string with the 4000US inverter, but that gets you awfully close to 600VDC (595VDC) at 14⁰F. You might want to play it safe and drop one of the modules. Unfortunately, none of the SMA inverters will operate with only 12 modules in a string (with two strings). However, a Fronius IG-3000 will, so you might want to go with that, although it has a lower efficiency. Brian Teitelbaum
AEE Solar
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joel Davidson
Sent: Tuesday, November 17, 2009 4:56 PM
To: RE-wrenches
Subject: [RE-wrenches] SWR2500U Inverter
Wrenches, Our customer has 24 each Kyocera KC130 modules and wants to go grid-tied.
Can he use an SMA SWR2500U inverter with the fan kit? Is there a better
inverter that will use all of his modules? If you have an SWR2500U or a
better inverter option for sale, please contact me off-list. Thank you very
much.
Joel Davidson _______________________________________________
List sponsored by Home Power magazine
List Address: [email protected] Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>

------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to