Lee,

 

Your idea about 2 strings of 16 is fine on a Fronius IG2000. The voltage is
correct and the inverter power is more than sufficient. There is no
difference at all in the way module bypass diodes were done then (early
1990s) as now. You want to check the Voc of each module to make sure there
are no failures, but beyond that, everything else is the same. They are not
on the CEC list because they predate the list.

 

Bill.

 

From: [email protected]
[mailto:[email protected]] On Behalf Of David Katz
Sent: Wednesday, November 18, 2009 1:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] strings of older solar panels

 

Lee
I would be inclined to use groups of 4 modules wired for 24 volts connected
to an Enphase inverter.  This will give you less problem with mismatch loss.
256 watts is high but they are probably a bit lower in output that that.
David

David Katz

Chief Technical Officer

AEE Solar

1155 Redway Drive

P.O. Box 339

Redway, CA  95560

Tel (707) 825-1200

Fax (707) 825-1202

[email protected] <mailto:[email protected]> 

www.aeesolar.com <http://www.aeesolar.com/> 

 

DISCLAIMER: 
This communication, along with any documents, files or attachments, is
intended for the use of only the addressee and contains privileged and
confidential information. If you are not the intended recipient, you are
hereby notified that any dissemination, distribution or copying of any
information contained in or attached to this communication is strictly
prohibited.  If you have received this message in error, please notify the
sender immediately by e-mail reply and destroy the original communication
and its attachments without reading, printing or saving in any manner.

 



Solar Plexus wrote: 

Hi Wrenches. 

 

 I have a customer with 32 of the Solarex MSX-64 solar panels an a
battery-based system.  He wants to go batteryless inverter.  So I am looking
at  2 strings of 16 in series.    But the solar panel spec sheet doesn't say
anything about system voltage rating.  Can I do this?

  If  one solar panel in the string is shaded, does it see the full string
voltage of around 280 volts?  Is there something in the way new panels are
made that makes them more able to handle this voltage, or is it just that
they are now tested for it?

 My guess is this request may be happenning a fair amount.  Is there a
reason these panels are not listed on the California GoSolr website?

 

Lee Tavenner

Solar Plexus

 



  _____  



 
_______________________________________________
List sponsored by Home Power magazine
 
List Address: [email protected]
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 
  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to