Thanks, Tom. I think I have seen those photos before.

Am I seeing 16 cables hooked up to each bus bar? Are you using 2 cables for 
each end of each string? Is that 8 series strings?

I can certainly see the advantage of being able to easily remove a string from 
the system.

But I still do not see how it will treat the individual batteries much better 
than using large parallel cable interconnects, which might be cheaper if the 
runs are not too long.


Tom Elliot wrote at 06:45 PM 12/2/2009:
 
>Michael,
>
>Here are photos of how it's done in a home situation 
>http://www.wagonmaker.com/newbatt2.html
>
>What is handy about the buss bar is the ability to use much smaller cable from 
>each series pair (in this case) to the buss bar, thus less expense in cables 
>than otherwise and additional expense for the smaller cables is far better if 
>it produces extended battery life and ease of service than the alternative.  
>The buss bars themselves are tinned copper bars mounted on stand-offs.
>
>Thanks to Jamie Surrette for confirming the wisdom of such setups.  I would 
>love to see battery companies beginning to provide hardware for such systems 
>and educating installers on how to use them.
>
>Tom
>
>
>--------------------------------------------------
>From: "Michael Welch" <[email protected]>
>Sent: Wednesday, December 02, 2009 2:00 PM
>To: "RE-wrenches" <[email protected]>
>Subject: Re: [RE-wrenches] Strings and series of batteries
>
>>
>>I wish I understood this bus bar use better. Electrically, these seem to be 
>>the same thing. But by using the bus bar, there has to be more cables, cable 
>>ends, and connection points. And cost.
>>
>>I just drew a battery bank (see below link to graphic), three series strings 
>>in parallel. On the negative side I drew a bus bar. On the positive side I 
>>drew normal parallel cable interconnects.
>>
>>The bus bar side requires 3 cables with 6 cable ends and 6 interconnection 
>>points.
>>
>>The cable side requires 2 cables with 4 cable ends and 3 interconnection 
>>points.
>>
>>How can a bus bar possibly be better? There will always be one more cable, 
>>and 2 more cable ends to connect.
>>
>>I do not see how either way could cause the current for one battery pass 
>>through another. It is merely using the terminal of the battery as a 
>>connector between two cables. Ditto for any difference in how internal 
>>resistance reacts, they both seem the same to me.
>>
>>Related question #2:
>>
>>It also has been noticed that some installers use "cross tie" interconnects 
>>for paralleling batteries in the middle of the series strings where the 
>>positive of one battery connects to the negative of the other -- not just at 
>>the final pos. and neg. outer ends of the strings. In fact, some even 
>>recommend two cables between:
>>http://www.green-trust.org/wordpress/wp-content/uploads/2008/09/cross-tied-battery-bank-300x187.jpg
>>
>>What's up with that? If it helps make charging equal, is it worth the extra 
>>expenses and connections involved?
>>
>>Here is a little jpg that illustrates both of these questions:
>>ftp://ftp.re-wrenches.org/pub/bbvscablewcrossties.jpg
>>
>>
>>
>>Tom Elliot wrote at 02:19 PM 12/2/2009:
>>
>>>Darryl, The process of paralleling through buss bars means attaching each 
>>>serial string to a pair of buss bars rather than to neighboring series pairs 
>>>so batteries aren't passing current through each other and aren't affected 
>>>by each others internal resistance.  The buss bars then feed the inverter 
>>>breaker.  It's standard practice in large telco installations which is where 
>>>I got clued into the process.  I got some batteries from a wholesaler who 
>>>did those installations and he was aghast at the idea of series/parallel 
>>>installations the way off-grid systems have been done traditionally.
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: [email protected]
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>
>
>>
>>No virus found in this incoming message.
>>Checked by AVG - www.avg.com
>>Version: 9.0.709 / Virus Database: 270.14.90/2540 - Release Date: 12/01/09 
>>21:33:00
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: [email protected]
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to