----- Original Message ----- From: "All Solar Inc. Jeremy Rodriguez" <[email protected]>
To: <[email protected]>
Sent: Tuesday, February 16, 2010 10:12 AM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup



Darryl,
I would say the utility is still learning.
10kw of PV to put into the grid or as large as 33kw if we can get this approved.
All 120V backed up loads.   We have 120/208.
The Xantrex XW?.
What do you mean by single phase backup.

Jeremy

----- Original Message ----- From: "Darryl Thayer" <[email protected]>
To: "RE-wrenches" <[email protected]>
Sent: Tuesday, February 16, 2010 9:50 AM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup


If you have 120/208 you have WYE. How much power do you have to put into the grid? The question if you need back up power what is it for? if it is simple plug loads or lighting you might serve the customer well with single phase backup. If you need 3-phase back-up I find it hard to accept that they need it in one box. The Xantrex is three seperate inverters on one board that looks like 1 box. The three 120 volt units make 120/208 three phase. If you have 120/240 three phase you have Delta, high leg. Other combinations of three phase are possible, but more rare.

I am old and I have never seen a problem of 3 phase imbalance if I stay within 20% of the panel rating. In fact I have seen single phase loads that will imbalance more than 20% not cause a problem. The problem of imbalance is similar to what occurs with single phase and changed inverter rules to requireing a ground reference on 240 volt inverters. This problem is that the neutral will get pushed off center voltage wise, I usually demonstrate this in my class. YOu can not cause significat imbalance with three 120 volt inverters, but you could woty the old 208 no neutral inverters.

Darryl

--- On Tue, 2/16/10, All Solar Inc. Jeremy Rodriguez <[email protected]> wrote:

From: All Solar Inc. Jeremy Rodriguez <[email protected]>
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
To: "RE-wrenches" <[email protected]>
Date: Tuesday, February 16, 2010, 9:27 AM



#yiv965209721 DIV {
MARGIN:0px;}




Yes,
No Transformers,
Single inverter.

Another question, looking
at the Fronius 10.1 and
11.4-3, no battery backup of course, they both list
208v in the sizing
tool. I need to look at a manual, but I'm not sure
if I would need
Delta, Wye, ..........

Thanks
everyone!



  ----- Original Message
----- From:
  Rebekah
  Hren
  To: [email protected]

  ; RE-wrenches

  Sent: Monday,
February 15, 2010 5:34
  PM
  Subject: Re:
[RE-wrenches] 3 Phase Grid
  Tie with Battery Backup




  Hi,
  Does the utility mean by "match" that they
don't want the inverter output
  transformed in any way?
  Could you not just use one 120V inverter? I've
connected single 120 volt
  inverters (albeit not outback but I don't see why
not) to a 120/208 wye
  without problems. You have to make sure the wires are
sized correctly (solar
  pro had a recent article on unbalanced 3 phase wire
sizing). This of course
  limits your backed up loads to 120V (w/out a
transformer).


  Rebekah Hren
  North Carolina









  From: Allan
Sindelar
  <[email protected]>
To: RE-wrenches
  <[email protected]>
Sent: Mon, February
15, 2010 6:51:12
  PM
Subject: Re:
[RE-wrenches]
  3 Phase Grid Tie with Battery Backup

Yes you would. I don't
  believe there is a single inverter that meets the
utility's wishes.








  Allan Sindelar
[email protected]
NABCEP Certified
  Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy,
  Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505
  424-1112
www.positiveenergysolar.com

All
  Solar Inc. Jeremy Rodriguez wrote:
  Thanks Darryl,
Allen, would you have to use 3
    Sunny Islands? one for each phase?
The Utility wants a single
    inverter.

Jeremy
----- Original Message ----- From: "Darryl
    Thayer" <[email protected]>

To: "RE-wrenches" <[email protected]>

Sent: Monday, February 15, 2010 3:49 PM
Subject: Re: [RE-wrenches] 3
    Phase Grid Tie with Battery Backup


I do not know what is going
    on at Outback, but unless they reduced the product
offering, they have the
    capability. I have such a system.

Use 3 of their 120 volt
    single phase inverters connected 3-phase WYE (120/208)
3 phase. Each
    inverter is only a single phase, and you connect each
inverter to the
    neutral and one phase, you program one to be the
Master, and the others to
    be slaves on phase B and Phase C. When you lose
the grid, the Master
    inverter starts its sine wave and it generates the
usual 60 Hz square wave
    on the Outback Bus and the following slave units delays
the start of their
    sin waves by the appropriate 120 degrees to generate 3
phases. Each
    inverter picks up and makes 60 hz 3 phase.

One thing, besure to get
    a rotation meter and check that you are generating
3-phase the same rotation
    as the grid. Else you will have big problems. (motors
will reverse and you
    may fry the OB transfer relay)

Next time you call outback ask a tech
    if you can slave the GVFX to make 3 phase,

--- On Mon, 2/15/10, All
    Solar Inc. Jeremy Rodriguez <[email protected]>
    wrote:


    From: All Solar Inc. Jeremy
Rodriguez <[email protected]>

Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery
Backup

To: [email protected],
      "RE-wrenches" <[email protected]>

Date: Monday, February 15, 2010, 4:14 PM
Jeff,
That was my
      first choice, but I was told by Outback
that they do not offer
a
      120/208 inverter(s). I have not set up a three
phase system yet, so
      bare
with me please. I was going to contact SMA next.

Jeremy



----- Original Message ----- From: "Jeff Oldham"
<[email protected]>

To: <[email protected]>;

<[email protected]>

Sent: Monday, February 15, 2010 3:03 PM
Subject: Re: [RE-wrenches]
      3 Phase Grid Tie with Battery
Backup


> You can also do
      it w/Outback up to 10.8kW
>
>>From the Solar, Wind and
      Hydro powered office of
Jeff Oldham/Regenerative
>>SOLutions









  _______________________________________________
List sponsored by
  Home Power magazine

List Address:
  [email protected]

Options &
  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List
  rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out
  participant
bios:
www.members.re-wrenches.org



-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to