Hi All,

I think it is clear that a fused disconnect is required next to the service 
tap. But I have one other thought.

When we install line side taps we always run the wire between the disconnect 
and service panel in rigid conduit and bond both sides of the conduit just like 
we would do with service wires. This is a requirement in San Francisco and come 
to think of it I haven't looked deep enough into the code to see if it is an 
actual NEC requirement or not. Thoughts?

-August

August Goers


Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
www.luminalt.com<http://www.luminalt.com/>

________________________________
From: [email protected] 
[[email protected]] On Behalf Of Bill Brooks 
[[email protected]]
Sent: Sunday, March 28, 2010 10:04 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

Dave,

All line side connections must have overcurrent protection (230.91) at the 
disconnecting means. Article 230.70 through 230.95 is what generally governs 
these connections. Without rewriting John Wiles’ articles on this subject, here 
are a few quick pointers.

The basic rule to remember, since you don’t have your code book, is to install 
a disconnecting means with overcurrent protection adjacent to the existing 
service. No specific distance is given, but the implication, and the field 
experience is as close as physically possible to the existing service 
disconnecting means. Circuit breakers or fused disconnects are allowed if they 
are listed as service equipment. Fused disconnects are used more often than 
circuit breakers since many utilities require a visible-break switch.

To give Xantrex the benefit of the doubt, their manual probably was not 
intended to address line side connections. If it is intended to cover these, 
there statement may be accepted by some jurisdictions, but it quite unlikely 
that a jurisdiction would ever allow it. To have line side conductors, with no 
disconnecting means, installed into a PV inverter wiring center just doesn’t 
make sense. Always install a service disconnect with overcurrent protection on 
every connection to service conductors—that seems like a logical and simple 
rule that can never go wrong.

Bill.

From: [email protected] 
[mailto:[email protected]] On Behalf Of Dave Palumbo
Sent: Sunday, March 28, 2010 10:53 AM
To: 'Wrench List'
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

Wrenches,

I am tasked with reviewing an installation by a licensed electrician in Vermont 
and would like help with the following:

Grid-tied PV system with battery back-up. AC point of connection is a supply 
side tap (done on customer side of utility meter ) then traveling 5 feet of #2 
THHWN in 1” EMT to the 60 Amp 240vac Lockable Utility Disconnect (unfused) and 
continuing 15 feet #2 THHWN 1” EMT to Xantrex XW 60 Amp breaker.

I had said that the 60amp 240vac lockable disconnect needed to be fused, and 
received the following reply from the installing electrician.

<< “The Xantrex XW Power Distribution Panel contains the required over current 
protection (60 amp
double pole circuit breaker) negating the need for a redundant fuse at the 
Utility Disconnect switch.” >>

I am on a short trip in Florida and away from my code books. Can someone 
provide guidance and code reference please? I am concerned about the 20 foot 
distance of the un-protected circuit from the supply side tap and also the 
interrupt rating of the 60 Amp breaker in the Xantrex distribution panel.

David Palumbo
Independent Power LLC
Offices in Lamoille and the Champlain Valley
802.888.7194
www.independentpowerllc.com

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to