Thanks Robin.  I've long been suspicious that the CBI circuit breakers should not be run at 100% for a couple reasons:
1) I've seen too many 60-amp CBI breakers on charge controllers trip habitually.  But a replacement 60-amp breaker works fine.
2) Nothing in the CBI literature that is available on their web site says the QY breakers are rated to operate at 100%.
The published trip curve shows that the breaker is supposed to hold at less than 105% of rating and trip at more than 130% of rating. 
The trip curve for a QO breaker shows that it is supposed to hold at 100% of rating and trip at 130% of rating too.  Yet we know that it is not intended for continuous operation at 100% of rating. 

Kent Osterberg
Blue Mountain Solar, Inc.


boB Gudgel wrote:

Forwarding a message from Robin Gudgel...

Robin Gudgel wrote:
The CBI QY series of DC breakers have an arc shoot that is required to
quench a DC arc. This breaker would work just fine as an AC breaker although
is not marked as such. I am not sure if the AC breakers (QL, QZ and QZD
series) have the arc shoot. I was told years ago by CBI that the AC and DC
breakers are built the same, but I had never broke one open to see if the
arc shoot is present on AC breakers until today. The AC breakers do in fact
have the same arc shoot as the DC breakers. CBI just marks the outside of
the breakers differently. You don't want to get called on the AC vs. DC
issue by an inspector because you are going to lose that battle. It makes
things a bit confusing to have a DC breaker in an AC circuit even though
they are identical inside. I believe Allan Sindelar was in the field and had
a situation where it saved a bunch of time and hassle to use a QY breaker
instead of a QL that he did not have on hand. I had told him that the DC
breaker would function just fine as an AC breaker. That installation was
safe, but an inspector would probably make you change to an AC breaker.

I remember years ago seeing in print that a Hydraulic/Magnetic breaker could
be used at 100% duty rating where as a thermal breaker could only be used at
80%. I have searched and searched to find this written explanation again to
no avail. I thought it was in the NEC, but I now believe I was wrong. If the
NEC does not allow the use of H/M breakers to be used at 100% duty cycle,
then it just is not allowed. It is true that the H/M breakers are not
affected by temperature like thermal breakers are, but that in itself
doesn't overrule the NEC. I personally have been spreading this myth to
hundreds of installers for 10 years. I now believe I was wrong. Sure wish I
could find that written explanation from years ago! Perhaps it came from CBI
or some other circuit breaker manufacturer? (see below) Maybe an old version of the NEC?
The NEC is the top authority, so please use the same de-rating guidelines
for CBI as for thermal breakers.
Sorry for perpetuating this widely accepted myth.
 

PS.  Robin found this and thinks that this may have been one of the texts but still
does not override NEC requirements

From Heinamann:

Continuous operation at 100%current.
There is no such assurance with a thermal device, which may
fail to carry rated current when subjected to above normal ambient
temperatures. A Heinemann breaker rated at 20 amperes, for example,
will sustain 20 amperes, even at elevated temperatures. Derating
and other forms of temperature compensation are unnecessary.


Robin Gudgel
MidNite Solar

 






-------- Original Message --------
Subject:     Re: [RE-wrenches] DC wire sizing
Date:     Fri, 02 Apr 2010 16:35:49 -0600
From:     Allan Sindelar <[email protected]>
Reply-To:     [email protected], RE-wrenches <[email protected]>



Yes, they are 100% duty rated. Also, a little-known fact about the CBI breakers used by Midnite and Outback, gleaned from conversations with Robin Gudgel: because of this hydraulic/magnetic construction, all are capable of controlling both AC and DC, even if not listed as both.

*Allan** Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
*Positive Energy, Inc.*
3201 Calle Marie
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>



robert ellison wrote:
 
I believe that the breakers from CBI, Midnite and Outback are hydraulic / magnetic and may be operated at 100% While the derating applies to all others that are Thermal / magnetic,
 
Bob

On Fri, Apr 2, 2010 at 11:14 AM, Kent Osterberg <[email protected] <mailto:[email protected]>> wrote:

    Erika,

    You should refer to NEC 690.8 this information.  There are two
    issues that contribute to the 1.56 factor.  First is that the
    maximum current from the PV array is considered the short circuit
    current multiplied by 1.25 to account for higher than standard
    irradiance such as cloud edge effect, high altitude, and high
    operating temperature.  The second multiplier of 1.25 is because
    PV current is considered to be continuous.  All conductors (and
    breakers) operating continuously (over three hours I believe) that
    are subject to NEC rules are limited to 80% of the ampacity in
    Table 310.16.  The two 1.25 factors equals 1.56.

    For normal operation, wires selected under this criteria are
    conservatively rated.  But it is also the objective of the NEC to
    design power systems in a manner that they will remain safe under
    abnormal circumstances.

    Kent Osterberg
    Blue Mountain Solar, Inc.




    Erika M. Weliczko wrote:
   
    To my understanding the 156% on PV source and output circuits is
    related to the ability of PV to deliver more than rated and be
    continuous.

    Therefore, the wire has to be able to carry this current, so now
    the temperature and fill corrections are applied to find the wire
    capable of the 156%.

    
    I am in a debate where the question is why correct for temp and
    fill on 156% of ISC and spend all that extra money when the
    normal operating is at Imp. Or why correct the 156% but why not
    correct the Isc or Imp.

    
    I am going to stick to the fact that the circuit has to carry the
    156% under all conditions.

    Thoughts?

    
    Erika


     
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org/>



------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
   
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

     


 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.800 / Virus Database: 271.1.1/2787 - Release Date: 04/02/10 23:32:00

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to