>>Since the topic of AFI's has come up I wonder if anyone has actually tested 
>>one, even an AC one.
>>
>> From what I've read from some tests on the Mike Holt site for AC breakers is 
>> that they couldn't get them to work at anything less than standard ISC for 
>> the breaker.
>
>I've not tested them, but I have read every patent on AFCI technology I can 
>get my hands on.
>
>They don't sense that the load is arcing, in the sense -- say -- of an 
>electric motor which arcs because of how the brushes work, or any number of 
>other loads which arc.  What they detect is arcing current well above the 
>rated ampacity of the circuit breaker.  A "series" arc, where the arc is 
>passing through a load, is limited to the load itself -- a 12 amp rated vacuum 
>cleaner makes, maybe, a 12 to 15 amp spike when it arcs.  A "parallel" arc, 
>where the arc is passing directly from line to neutral, or line to ground (not 
>all AFCIs include ground-fault detection), will conduct up to the current 
>available from the transformer.  However, because it is not a constant load, 
>it doesn't trip the over-current protection of the breaker, the arc just sits 
>there until either it self-extinguishes or it causes a fire.
>
>There have been a lot of discussions on Mike's board about how useless AFCIs 
>are.  In the case of RE systems that have significantly less available current 
>(maybe 50 or 100 amps, rather than hundreds to thousands), it's unlikely that 
>a standard AFCI would "see" a high enough current to decide that a "parallel" 
>rather than "series" arc was happening.  But if the AHJ wants them, the AHJ 
>gets them ...
>--
>Julie Haugh
>Senior Design Engineer
>greenHouse Computers, LLC // jfh at greenhousepc.com // greenHousePC on Skype

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to