>I'd like to pitch in my experiences with the TED -- as others have pointed 
>out, it leaves some things to be desired.
>
>I have a client with a TED 5000 -- Holt Kelly from this list is the installer 
>-- and there were some limitations that haven't been resolved by Energy, Inc.
>
>The show-stopper for my client is that they have a hybrid system with a 
>SB6000U and GVFX3648.  The customer wanted to monitor the production of both 
>inverters.  The client has three CTs installed in their main panel -- one pair 
>around the feeders from the meter, another pair for the SB6000U and a 
>singleton for the GVFX3648.
>
>The problem is that only the first CT is configured to record bi-directional 
>power.  The result is that the GVFX3648 always shows up as a load, regardless 
>of direction of current flow.  The only solution to this limitation, right 
>now, is to configure that CT as a "Stand-alone" system.  It turns out that the 
>way their GUI displays the data, the SB6000's CT also needed to be configured 
>as stand-alone system.
>
>In terms of customer support, the people I spoke to (for two hours) do not 
>understand renewable energy systems, and do not listen.  The client has 8KW DC 
>total and the system was exporting a fair amount of that.  The CTs were 
>misconfigured (see earlier) and customer service didn't understand that my 
>client was NOT using 4KW or whatever.
>
>The TED 5000 is okay in a single CT configuration.  They've promised firmware 
>updates that will make it work better with inverters, but I'd hold out before 
>installing in a configuration that =required= that functionality.  In my 
>client's case, they wanted to know system net (import / export), and the other 
>two CT values are less important.
>--
>Julie Haugh
>Senior Design Engineer
>greenHouse Computers, LLC // jfh at greenhousepc.com // greenHousePC on Skype

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to