Im sorry, I meant to write “11 modules per string” below..
Been a long day..

From: Jim MacDonald
Sent: Monday, April 19, 2010 7:41 PM
To: RE-wrenches
Cc: Jason Szrom
Subject: RE: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

SB8000US only good for 480 Vac, we’re tying in at 208.

11 strings [11 modules per string] has been calc’d to be OK (<600vdc) for 
record low -4 fahrenheit (-20 celsius).

I think the big concern as mentioned is getting the Voc high early in the AM to 
wake the inverter up, also maintaining the Vmp later in the day to keep it 
running for as long as possible into the late afternoon/ evening.
Will those extra kWh gleaned in the early AM/ late PM over the course of 365 
days be more than the kWh clipped during peak production times with the 9.075 
kWdc?
NYC average summer highs between 79 and 84 fahrenheit early june-late august.  
Sunlink rack @ 10° on a silver-painted built-up roof.

Time-of-use utility $ peak-shaving is not an issue here.

Thank you




From: [email protected] 
[mailto:[email protected]] On Behalf Of Darryl Thayer
Sent: Monday, April 19, 2010 5:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

The temperature correction is the concern.  I have heard lots of stories of 
inverters dieing when it gets to cold.  Look in the code book 690.7 at the 
temperature correction table.  Go to weather.com and find your record low 
temperature.  Find you Tc factor and will your senerios work?  I have heard 
from a sunny boy rep that it is OK to over power by 1.25%
darryl

--- On Mon, 4/19/10, Dana <[email protected]> wrote:

From: Dana <[email protected]>
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?
To: "'RE-wrenches'" <[email protected]>
Date: Monday, April 19, 2010, 4:31 PM
Many times we switch to another module manufacturer as one will not fit or 
another inverter manufacturer.
PVPowered has a more relaxed window and we have had fine success with them when 
SMA does not fit.
Cold is the dictator and the 600 VDC threshold.


Thanks,  Dana Orzel

Great Solar Works, Inc
web - www.solarwork.com
E - [email protected]
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076

"We have been slow to give up on the myth of the Earth's generosity.
Rather grandly, we have overdrawn our accounts."
Barbara Kingsolver - Water is life.

From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: [email protected]
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little shade, 
NYC avg 4.29 kWh/m²/day.

Feed an SMA7000 with (3) strings of 11 Suntech STP275’s [9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.

Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp

The tradeoff would be power clipping at/around noon in the sunny months in the 
9.075 kW scenario;
Inverter sleeping late every morning and retiring early in the evenings in the 
lowered voltage scenario.

Trying to figure out which would yield more kWh at the end of the year.

Any ideas appreciated,
thanks




Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.com<http://www.solaresystems.com/>


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10 
00:31:00

-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<http://us.mc519.mail.yahoo.com/mc/[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to