Allan,
Are you running 100+ volts DC through a Square D breaker? They are not
rated for anything above 48VDC. Midnite Solar makes a manual transfer
switch that can be fitted with 150 VDC breakers. That may be a better
choice.
David
David Katz
Chief Technical Officer
AEE Solar
1155 Redway Drive
P.O. Box 339
Redway, CA 95560
Tel (707) 825-1200
Fax (707) 825-1202
[email protected] <mailto:[email protected]>
www.aeesolar.com <http://www.aeesolar.com/>
DISCLAIMER:
This communication, along with any documents, files or attachments, is
intended for the use of only the addressee and contains privileged and
confidential information. If you are not the intended recipient, you are
hereby notified that any dissemination, distribution or copying of any
information contained in or attached to this communication is strictly
prohibited. If you have received this message in error, please notify
the sender immediately by e-mail reply and destroy the original
communication and its attachments without reading, printing or saving in
any manner.
Kent Osterberg wrote:
Allan,
Here the electrical inspector won't let us install the CU-200 or other
SQFlex controls because they are not UL listed. The pump is not
listed either, but he doesn't object to that. So I've installed the
SQFlex pumps using a pair of SQ D QO breakers with interlock kit so
they can be run on a generator or solar system. To turn them off, a
2-gallon pressure tank with pressure switch (adjusted to operate at 10
psi) works great if the PV array is near the pumping system.
Kent Osterberg
Blue Mountain Solar, Inc.
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org