[email protected] wrote:
Don't you think the transformer is good for isolation?

Todd

I like transformer isolation, but I suppose as long as the neutral of the generator is
tied to ground and battery negative you'll be OK.

As far as capacitors go, there is usually plenty of capacitance built into on the PV input of MPPT charge controllers already. At least the ones I have seen, there's LoTs of C.

boB




On Tuesday, April 27, 2010 4:26pm, "ryan" <[email protected]> said:

> I have done this a couple times. I have done this with a MX60 and a
> MidNite Classic the beauty with the Classic is you can eliminate the
> Transformer. I Simply rectified the 120vac and fed it into the Classic
> works like a charm. I ran about 30 to 40 amps output into a 24 volt
> battery bank. There has been some discussion about using some Caps to
> filter the dc after rectification but I have never messed with it.