Hey Bill,

Two MPPT charge controls from different modules in parallel to one battery pack - do they settle into one voltage or do they sweep each other and constantly search? Do they need to be identical controllers - what if they have different algorithms?

Jeff C.
Village Power Design



Content-Type: multipart/alternative;
        boundary="----=_NextPart_000_00B3_01CAE722.85B5A9E0"
Content-Language: en-us

Allan,

My beard is pretty gray these days, so I'll bite. Without getting deep into exactly where these modules have degraded to, I think your idea of adding the extra MSX77s is a good one, although it might be a little overkill. Since the customer has them, I would use them.

The other issue is that newer modules may have a better temperature coefficient of voltage than the old Solarex modules. The SolarWorld 175 will not lose as much voltage at the same temperature. If you can split like modules on their own MPP charge controllers, that would solve your problem-Not sure that is an option for you.

Bill.

From: [email protected] [mailto:[email protected]] On Behalf Of Allan Sindelar
Sent: Wednesday, April 28, 2010 12:20 PM
To: RE-wrenches
Subject: [RE-wrenches] Solarex module match question

Calling the old-timer off-grid 12V graybeard Wrenches...
I am reposting this to the list in hopes of shakin' up a response, as nobody tried to answer my request for help.

In short: in theory, if you force an array to operate at a voltage above its MPP, current drops off significantly on the string I/V curve. In this case, if I add a fixed array of substantially larger current and slightly higher Vmp (due to both what's currently available having a slightly higher module Vmp, and 14 years of module degradation), will the new array force the old array to operate at too high a Vmp and thus substantially reduce its contribution to overall PV input?

And a related question: the customer reminded me that he still had two additional matching Solarex MSX77 modules stored away. If I could mount them on the existing 12-module Wattsun tracker, and if I wired them as two strings of seven modules (84Vnom), would that solve this issue, by boosting string voltage enough to maintain current closer to Isc?

I'd appreciate any good advice.
Allan

Original post:

Wrenches,
We have an off-grid customer with a system that has been growing since 1996; we have cared for it intermittently since 2000.

The customer has two tracked arrays currently. One has ten Astropower AP120s for 1200 nominal watts, but that's not the topic today; it'll come up in 5 years or so. The other older array is 12 Solarex MSX77s, polycrystalline with 16.9Vmp, 21Voc (when new). The rest of the system is a SW4024, two Solar Boost 50s (one is currently failing) and two strings of 800 a/hr Rolls cells.

The client wants to add 1,200 to 2,000 watts of additional PV. The problem is that we have two sets of existing buried conductors between arrays and BOS and don't want to dig up for more. Also, he wants to upgrade charge controllers, and has had past failures of the SW inverter - in fact, he keeps a spare put away for the next failure.

I have suggested that by upgrading the inverter to a modern pure-sine 48V unit, we can accomplish the array upgrade using the existing input conductors. I can rewire the Solarexes from 6 24Vnom strings to two 72V strings and have plenty of copper to add more array without voltage drop issues. (The AP120s can be brought in as 2 60V strings to a separate FM60 or T80 or similar). This also lets me work with existing 60 or 80A charge controllers, which I can't do at 24V.

The customer likes this approach, so here's my question: What modules would you suggest as having good compatibility with the existing Solarexes? I would assume that any polycrystalline 72-cell module would be fairly close but not ideal. I would especially expect the lower-rated ones within a particular size category to be better choices, as they would have lower Vmp to more closely match the existing. But would similar monocrystalline be close enough? Too high a voltage in the dominant (new) array drags the voltage above MPP, which reduces output considerably on the Solarexes. Also, I can't find the temperature coefficient for the old modules, and I suspect that degradation over 14 years has lowered the MPP of them anyway.

I think of using 12 Kyocera KD135s Mitsubishi 125s or 130s; Solarworld's discontinued SW175 (mono), Sharp 123s, or possibly some Suntech monos. But I'm certainly open to advice and suggestions here.

Also, while the existing arrays are on Wattsun DA trackers (customer's choice), the new array will be pole-top. I'm not too worried about tracking/fixed mismatch, as voltage quickly matches even with non-optimal orientation. But I'll take advice here too.


Thanks.
Allan
--

Allan Sindelar
<mailto:[email protected]>[email protected]
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
<http://www.positiveenergysolar.com/>www.positiveenergysolar.com

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


--
~~~~~~~~~~~~~~~~~~~
Jeff Clearwater Lernould
Village Power Design

Solar Design Consultation for the Commercial Sector
http://www.villagepower.com
[email protected]

NABCEP Certified Solar PV Installer 
http://www.nabcep.org/

Voice: 831-427-2799
Fax: 413-825-0703
245 Dufour St
Santa Cruz, CA 95060
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to