Esteemed Wrenches,

I'm in the process of bidding a small government job. They're requiring the following tests. I was wondering if any of you have ever run across this before and if so how you went about it.

/- Inspect inverters according to requirements in NETA Acceptance Testing
Specifications.

- Test the PV system under prime solar design conditions to validate system power performance rating. Use instruments calibrated within the previous six months according to NIST standards. /(not easy since the site they've chosen will shade some of the array all the time. I should be able to just explain this to them)
/
- Simulate malfunctions, including ground faults, to verify protective device
operation.   /(I would create a GF and then replace the fuse for this test)
/
- Test anti-islanding shutdown function due to normal utility source failure, time delay and automatic restart after utility power restoration. /(this is an easy one)
/
- Test and record the total harmonic distortion (THD) content of output
current at 25, 50, and 100 percent of system rating.  Comply with IEEE 519
at MDP point of connection.

- Test and record the real power output for each inverter, and total power
delivered at the grid tie connection, for a 24 hour period.  The continuous
power output during prime solar conditions shall meet or exceed
performance requirement under part I of this specification.

- For each inverter, record DC input voltage for 24 hours, to demonstrate
affects of maximum power point tracking (MPPT), voltage regulation within
inverter rated limits, and affect of partial shading on solar modules. Simulate partial shading by covering 50% of modules during prime solar
conditions.

- Record of Tests and Inspections: Prepare and submit documentation of tests and inspections, including references to manufacturers' written instructions and other test and inspection criteria. Include results of tests, inspections, and retests.

/
Any advice would be gratefully accepted and appreciated!

Best,

Greg Egan

NABCEP Certified PV Installer
Remote Power Inc.
Fairbanks, AK

--
Greg Egan

Remote Power Inc.
981 Gold Mine Trail
Fairbanks, AK 99712
P. 907.457.4299

U.S.Distributor for Outback Power Systems and other premium power equipment.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to