Hi Bob,

I run into this issue nearly every week and the solution is the same every 
time: install a small dedicated inverter. CPAP machines and cell phone chargers 
work just fine with modified square wave inverters but for only $100 you can 
have a 300 watt sine wave inverter. I'd recommend sine wave since many small 
load items like battery chargers, electric blanket control, electric 
toothbrush, etc., fail with MSW inverters.

Contact me off list if you don't have a resource for small 12, 24 and 48 volt 
inverters.

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103

Mailing Address:
11881 S. Fortuna Road, #210
Yuma, AZ 85367

Retail Store & Shipping Address:
2998 Shari Ave.
Yuma, Az 85365


  ----- Original Message ----- 
  From: bob 
  To: 'RE-wrenches' 
  Sent: Tuesday, May 11, 2010 8:58 AM
  Subject: [RE-wrenches] Tiny load problem


  I am sizing a system that will have dual inverters to shorten generator 
charging in the winter and enough solar to charge the rest of the time. 

  Here's the problem, the inverter will not be able to get into sleep mode at 
night.

   

  There are 2 cell chargers and a "cpap" machine having to run all night.

  It only totals 26 watts, has anyone found a better way to do this without 
having to keep an inverter awake to produce 26 watts?

  I would like to dedicate a Morningstar 300 watt inverter for the job but the 
system is 24 volts and Morningstar has no plans to make one in 24 volts.

   

  Anyone got any other ideas, or am I best to just deal with it?

   

  Thanks,

  Bob
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to