Hi,One thing to be clear about is whether these are listed for "48 volt 
systems," or for max 48 volts?I was under the impression that they were max 48 
volts, meaning you really shouldn't use them on a system >24volts nominal.
Rebekah HrenNorth Carolina 

http://thecarbonfreehome.com/

--- On Sat, 5/15/10, Kurt Albershardt <[email protected]> wrote:

From: Kurt Albershardt <[email protected]>
Subject: Re: [RE-wrenches] AC breakers used in DC applications
To: "RE-wrenches" <[email protected]>
Date: Saturday, May 15, 2010, 12:59 AM

The Square-D catalogs are marginally clear on which breakers are listed for DC 
and for what voltages, but when I tried to select an appropriate load center 
for a DC application earlier this year I quickly ran into a number of conflicts 
in their catalogs.  Here is the response from Schneider tech support 
(Case# 4845778 on 1/19/10 in case anyone runs into problems with an inspector):


The load center catalog numbers listed below are UL LISTED, File E6294, for use 
on 48 V dc systems. The load centers listed ARE NOT MARKED for use on this 
voltage system, however are suitable for the application. QO branch breakers, 
10-70 ampere (1 and 2 pole) are also UL LISTED for use on 48V dc systems. Short 
circuit current rating is limited to 5,000 amperes when used on 48V dc.
QO24L70F, S or RB QO612L100F, S, DF, DS, DFCU, DSCU, RB, TRB or RBCU 
QO816L100F, S, DF, DS, DFCU, DSCU, RB or RBCU
QO112L125G or QO11224L125G QO116L125G QO11624L125G QO120L125G QO12024L125G 
QO124L125G or QO12030L150G QO124L150G QO130L150G or QO112L200G or QO130L200G or 
QO13040L200G QO142L225G or
GRB or GRB
or GRB
GRB
GRB GRB GRB or GRB QO142L225GRB

I can email the PDF to anyone who needs a copy.
 

On May 13, 2010, at 18:24 , Darryl Thayer wrote:
I thought the Sq.D QO for sizes up to 60 amp was rated for DC?  and only the 
Square D  
Also why not use DC breakers? Robin makes some very small breaker boxes, and he 
alos has high voltage breakers,  (at least 250 volt? DC)
Darryl

--- On Thu, 5/13/10, William Miller <[email protected]> wrote:

From: William Miller <[email protected]>
Subject: Re: [RE-wrenches] AC breakers used in DC applications
To: "RE-wrenches" <[email protected]>
Date: Thursday, May 13, 2010, 7:18 PM


 
Bill:


I thought the rule of thumb was:  Don't do it.


William Miller





At 05:10 PM 5/13/2010, you wrote:

 

Fellow Wrenches,

 

Some time ago, Windy Dankoff had a rule of
thumb to substitute (conservatively) an AC breaker for use in a DC
application. 

 

Is anybody's memory, or perhaps even the old
dog himself; if he is listening, better than mine?

 

TIA,

 

Bill Loesch

Solar 1 - Saint Louis Solar

314 631 1094 

-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org










      _______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to