Hi Bill,
The valves are the AM-1 series. I wasn't aware that these incorporate check valves. In fact, we have had problems in some systems having HW recirculation with the hot circulating back through the cold supply, causing us to install separate check valves in the cold lines (which we install as standard practice, now). The specifications say, "Check valves, as indicated, may be installed, to prevent migration of hot water into the cold branch, and cold water into the hot branch through the SparcoMix Valve". The "indicated" check valves on the spec schematics are external to the AM-1 mix valve. Are integrated check valves a relatively new feature? My specs are old, and we haven't installed any new valves within the past year or so.

I have seen the "crossover" problem on some systems. I don't think that is the cause, here. I have (calibrated) temp gauges on the hot and the mix lines right at the mixing valve to see what's going out. I suspect THAT is the problem - I can SEE that it's not working right, whereas most people don't know and just adjust the temp at the faucet......

-Kelly
Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
[email protected]
360-678-7131


On May 20, 2010, at 4:29 AM, Bill Loesch wrote:


Hi again, Kelly,

You mentioned backflow issues in your post, which I should have addressed
with my previous reply.

If the Honeywell valve you are using is a Honeywell AM-1 Thermostatic Mixing Valve it incorporates dual check valves on the inlets. Those check valves are removable and those check valves are also susceptible to scaling if the
water quality is deficient. (See previous post.) The AM-1 has a Teflon
coating which would delay the effects of scaling, but would ultimately
succumb. The integrated check valves as well as the mixing valve itself,
will also produce a pressure reduction in the system.

A phenomena known in the plumbing trade as "plumbing crossover" and perhaps
more descriptively labeled as plumbing bypass, is the situation where
(typically) the cold water flows into the hot water side. This can be
illustrated with the homebrew shower where the throttling valves on the hot
and cold lines are supplemented with a third valve to allow the mixing
(throttling) valves to remain preset and the shutoff is downstream of the two mix valves. This is an excellent written illustration and relatively obvious. Unfortunately, what is much more common is the not so obvious, widespread use of single handle faucets. Once the seals on the cartridge, module, insert (terminology dependent on manufacturer) become worn, the same
situation exists with the single handle faucet as described with the
homebrew three valve shower.

The easy test for this condition is to stop the flow of hot water at the source, then open all hot water faucets. _Any_ flow, at any faucet, after a
delay to allow gravity drainage to occur, would indicate a plumbing
crossover/bypass _somewhere_ in the system.

Some single handle faucets also incorporate dual check valves into their construction. Again, poor water quality can render those inop in either or
both directions.

Thanks for your interest in getting a solution to this pesky problem.

Bill Loesch
Solar 1 - Saint Louis Solar



----- Original Message -----
From: "Kelly Keilwitz, Whidbey Sun & Wind" <[email protected]>
To: "RE Wrenches listserve" <[email protected]>
Sent: Wednesday, May 19, 2010 1:14 AM
Subject: [RE-wrenches] SWH - mixing valves


Thermal wrenches,
I'm having an ongoing issue with mixing valves in my own system not
keeping a steady mix domestic HW temperature as the tank temperature
varies with solar heating. If I set it for (say) 122˚F mix when the
tank is 135˚, it seems to hold that differential at all tank temps -
i.e. when the tank is hotter the mix is too hot (sometimes dangerously
so), and when colder the mix is too cold for a comfortable shower.
Thus, I need to change the setting all the time.

I'm now using a Honeywell valve with a 100˚ - 145˚ range. This is a
replacement for a valve with a wider range that acted the same way.
Any ideas,  suggestions for better valves, or....?

This has me wondering how many of our SWH customers are experiencing a
similar thing, but just aren't bothered enough to say anything. We
seem to have encountered many plumbing situations where the mixing
valve allowed weird backflow or siphoning situations to mess with
system operation, especially with HW recirculation. I thought I had
all such causes eliminated on my system, but maybe not.

Thanks for sharing your experience with such matters.
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
[email protected]
360-678-7131




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to