HI Mick,

The C-40 tries to hold an equalizing voltage for 4 hours to "complete" the 
action. With a system such as you described:  big, old bank of questionable 
functionality, the c40 could live forever in equalize mode. 



-Wes Kennedy

303-653-3073
NABCEPian

--- On Fri, 5/28/10, Mick Abraham <[email protected]> wrote:

From: Mick Abraham <[email protected]>
Subject: [RE-wrenches] Mystery: C-40 controllers "stuck" in EQ mode
To: "RE-wrenches" <[email protected]>
Date: Friday, May 28, 2010, 9:17 AM

Hi, Detectives~

At a client's off-grid home I observed two side-by-side Trace C-40 PV 
controllers, circa 1998, which were "stuck" in equalize mode. Day after day 
they did the red/green blink and they would not throttle back the incoming 
solar energy. This was with the jumper set for automatic EQ (should have been 
once per 30 days). I changed the jumpers to Manual EQ and normal behavior 
ensued: green blink with proper throttle back.



Clues: The battery is huge compared to the solar recharge current. The battery 
is also old and may have high self-discharge. Internal shorts in one or more 
battery cells are also possible. Because of these factors, the battery voltage 
was not reaching a high value even though the controllers were running wide 
open.



I thought that when the sun set, any auto EQ behavior on the C-40 would cease, 
but that didn't happen in this case. A product failure seems non-likely unless 
they both happened to break in the same way. Is there some other condition 
which the C-40 must see in order to be satisfied that it's OK to end the EQ?



Thanks in advance for helping me solve this mystery,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to