We've had no problems with Outback inverters and AFCI breakers, other than the 
inverter can't actually generate the 70 amps necessary to make an AFCI trip. 
(an inspector's AFCI tester didn't trip when expected) I think there should be 
an exception to the AFCI requirement, when the power supply max surge is less 
than 70 amps.
As soon as I know its new construction requiring AFCIs, I spec a sine wave 
inverter. 
I still like the old mod sine inverters (cheap, reliable, great surge, more 
efficient than sine) but they're probably only appropriate for old 
construction, small (uninspected) cabins, portable applications, and the third 
world at this point.
Especially now that Xantrex's TR series doesn't appear to be as reliable as the 
old DRs, we're not specing Mod sines much these days.

R. Walters
[email protected]
Solar Engineer




On Jun 1, 2010, at 11:51 AM, Kent Osterberg wrote:

> I recently talked to the tech support folks at Magnum about AFCI breakers and 
> they didn't know of a single one that would work with modified square wave 
> inverters.  The AFCI requirement for all new residential construction may 
> finally be the death of modified square wave inverters.  
> 
> Kent Osterberg
> Blue Mountain Solar
> 
> 
>> ----- Original Message -----
>> From: [email protected]
>> To: RE-wrenches
>> Sent: Monday, May 31, 2010 6:32 AM
>> Subject: [RE-wrenches] Arc fault questions.
>> 
>> Can & will someone explain, why off grid inverters will cause nuisance 
>> tripping of the AF receptacle. 
>> Does anyone have "real" field information as to how this might be reduced or 
>> eliminated? How about  which AF receptacles are less likely to trip? 
>> TIA tump
>> Sent via BlackBerry by AT&T
>> _______________________________________________
>> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to